answersLogoWhite

0


Best Answer

In an emergency it will heat half your oven or half your water heater because you only have half the supply voltage. The wattage must still meet the demand for the half power, Some special connections may be necessary to use 110 temporarly on the 220 circuits.

User Avatar

Wiki User

15y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

15y ago

Only if they are in phase and are reverse polarity. If the two 110v lines are the same polarity, then adding them together equals 110v. If they are reverse polarity (one is positive 110v and one is negative 110v), but are perfectly in sync (the two waveforms peak at exactly the same time) then the total voltage equals zero volts. Only if the waves are out of sync (one begins as the other ends) will you get 220 total volts.

This answer is:
User Avatar

User Avatar

Wiki User

13y ago

Your breaker box has two bus bars each with a different 120 VAC supply. Every other breaker is on the same 120 VAC bus. A typical 220 VAC breaker rests across each bus. So using two adjacent breakers, stacked vertically, will provide 220 VAC across the terminals of each breaker will supply 220 VAC. To be safe you want both breakers to trip if there is an over current situation and some breakers have a way to tie together the toggle handles of adjacent breakers to ensure this happens.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Can you put two 110 wires from different breakers together to get 220?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What happens when two wires are connected?

Wiring to the circuit breakers is 220 volts. The circuit breaker box has 2 110 Volt lines. If you connect two black lines together from one side nothing happens. If the these two black wires are from different circuit breakers you may have a safety issue by back feeding the electricity. If you connect 2 different 110 volt lines you will end up with a short. This ends up as a 220 volt short.


What happens when two hot wires are connected?

Wiring to the circuit breakers is 220 volts. The circuit breaker box has 2 110 Volt lines. If you connect two black lines together from one side nothing happens. If the these two black wires are from different circuit breakers you may have a safety issue by back feeding the electricity. If you connect 2 different 110 volt lines you will end up with a short. This ends up as a 220 volt short.


How do you split up a 240 volt outlet for 110 power?

A 220 outlet will have one neutral (white) and two hots (black and red normally) just use the neutral and just one of the two hot wires. Careful where you do this because normal 110 breakers are 15 or 20 amp and normally 220 breakers tend to be either 30 amp for a dryer or 50 amp for a stove.


How can I install a 110 receptacle alongside a 220 receptacle using the 220 receptacle wires for power?

While you can physically do this it violates the Electrical Code. 110 Volt and 220 Volt receptacles are required by the Electrical Code to be on separate breakers for safety reasons, this would put them on the same 220 Volt breaker.


What are the steps in connecting 120V to a 240V 60A air condition panel?

you should have three wires into the panel. two of them go to the double breakers or pull switch and the last is the ground lead. You can pick up 110 vac from one side of either breaker and that ground connection. DO NOT connect to the both breaker wires as that will be 220 vac


How many watts does a garage use?

Let's start with a typical 110 VAC service. You probably have 20 amp breakers in the service in the garage, and with at least 2 breakers, we have some idea of the theoretical electrical consumption. Remember, Volts X Amps = WATTS, so 110VAC X (2 breakers X 20AMPs) = 110 X 2 X 20 = 2200 WATTS


What prime number to you times together to get 110?

They are: 2511 = 110


Wiring diagram 110 quad?

i think its the red and black wires


How many wires are needed for 110 volt?

Hot, neutral and ground.


How many wires supply electricity to your home?

There are three wires supplying power to your home two line wires @ 110 volts each and one nutral.


How many 110 volts can be ran on one breaker?

One breaker in the North American electrical system will supply 110 volts. Two adjacent tied breakers will produce 220 volts.


What does a circuit breaker look like for 110 volt?

Most of the breakers in a panel will be 120 VAC. Double height breakers are 240 VAC. A triple height breaker probably indicates you have 3-phase power in the panel.