answersLogoWhite

0


Best Answer

I'm going to assume you are referring to residential construction because rules for commercial and industrial settings can be different. Also rules differ by geography (i.e. Canada specifies a maximum of 8 outlets on a 15 amp circuit, USA code is silent on the issue but for practical purposes, more than about 10 will likely lead to poor performance. Some code also specifies max loading of a 20 amp circuit at 80% making 10 outlets the practical limit if using 20 amp outlets on that circuit.

To expand on the previous answer a little, there is a large margin of safety in the construction of these components but if you think about it, you are placing a component that is rated at 15 amps into a 20 amp circuit. That outlet is potentially the weakest link in the circuit and could act like a fuse. If any of those 15 amp outlets are overloaded, it might overheat and fail before the circuit breaker. This is a recipe for a fire. You may think now that you'll remember to only plug in light loads, but these things have a habit of growing.

You can plug typical small home appliances (lamp, stereo, TV, etc.) into a 20 amp outlet so the only benefit in using the 15 amp outlet is the minor cost savings at installation. If it were my building, I wouldn't risk it.

If I can't talk you out of doing this and it's allowed by your applicable code, make sure you don't daisy-chain the circuit through the outlets. (In other words, don't run your 12-2 wire in one side of the outlet and out the other side.) Instead, use a pigtail (short piece of wire) to tap off your line to each individual outlet.

<><><>

In the United States you can run 20 amp breakers with 15 amp outlets but not in Canada. And for how many? About 10 to be on safe side as long as they are all low amp usage appliances. TVs, steros, fans, lamps.

<><><>

You can run 20 amp breaker with 12-2 wire as long as you make sure you use the 12-2 wire that is rated at 20 amp.


Whilst this was not your exact question it is worth saying IT IS NEVER SAFE to run a 20 amp load through a 15 amp receptacle. It is only rated to handle up to 15 amps.

<><><>

As always, if you are in doubt about what to do, the best advice anyone should give you is to call a licensed electrician to advise what work is needed.

Before you do any work yourself,
on electrical circuits, equipment or appliances,
always use a test meter to ensure the circuit is, in fact, de-energized.

IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOB
SAFELY AND COMPETENTLY
REFER THIS WORK TO QUALIFIED PROFESSIONALS.

User Avatar

Wiki User

14y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

14y ago

Yes. The breaker can be smaller, but not larger than the circuit it is protecting. The situation you describe would normally be protected by a 20A breaker, but what you suggest is fine. You couldn't go the other direction and use a 30 A breaker because it wouldn't protect the lesser rated components.

This answer is:
User Avatar

User Avatar

Wiki User

11y ago

It depends on if you have a single outlet (receptacle) on a branch or multiple receptacles on a branch.

One receptacle on a 20A branch: The receptacle must be rated 20A

Two or more receptacles on a 20A branch: The receptacles can be 15A or 20A

Technical Reference: 2011 NEC

210.21(B)(1)A single receptacle installed on an individual branch circuit shall have an ampere rating not less that that of the branch circuit.

210.21(B)(3) Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in Table 210.21(B)(3), or, where rated higher than 50 amperes, the receptacle rating shall not be less than the branch circuit rating.

Table 210.21(B)(3)

20A Circuit Rating 15A or 20A Receptacle Rating

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Can you use 15A outlets on a 20A circuit with 12-2 wire and a 20A breaker and how many outlets would this allow?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

How many outlets and lights on a 60 amp breaker?

120 amps The above answer is wrong. A 60 amp breaker is designed to trip at 60 amps be it a single pole, double pole or a triple pole that is used on three phase equipment. The number on the handle of a breaker is the trip capacity.


What would cause a short periodic low hum to come from a circuit breaker?

A bad circuit breaker. Replace it.


What would happenif you put an 8 amp circuit-breaker in a power circuit?

The circuit would be protected up to 8 amps before the breaker would trip. Any more that 8 amps and the circuit would open and shut the circuit off.


What is an example of a circuit interrupter?

An example of a circuit interrupter would a fuse or circuit breaker.


How many oulets in a 15 amp breaker circuit?

Branch circuit loading In Canada the CEC states that there shall be not more than 12 outlets on any 2-wire branch circuit. These outlets shall be considered to be rated at not less than 1 amp per outletWhere the connected load is known, the number of outlets shall be permitted to exceed 12, provided that the load current does not exceed 80% of the rating of the over current device protecting the circuit. For example on a 15 amp breaker, 15 x 80% = 12 amps, hence the standard of 12 outlets on any 2-wire branch circuit.On a 20 amp breaker, 20 x 80% = 16 amps. So from a 20 amp breaker this allows 16 outlets on a 2-wire branch circuit as long as the outlets are not considered to be rated at less than 1 amp per outlet.The definition of an outlet is a point in the wiring installation at which current is taken to supply utilisation equipment. What this means is that if a light switch and a fixture outlet were on the same 2-wire branch circuit they would be subtracted from the maximum count of 12 receptacle outlets on the circuit which would leave 10.If the light fixture draws 3 amps plus the switch outlet, then the total circuit outlet count would be reduced to 8 receptacle outlets (12 &ndash; 3 &ndash; 1 = 8).On a standard specification home most electricians will wire one circuit per room, the outlet count usually never reaches the maximum of 12 outlets.

Related questions

Is a ground fault indicator outlet installed at the breaker box?

There are tow places to put a Ground Fault Circuit Interrupter. There is a GFCI breaker which would be installed in a breaker box and a GFCI outlet that can be installed anywhere. Most GFCI outlets allow you to connect regular outlets to the GFCI and those outlets will also be protected.


How many outlets and lights on a 60 amp breaker?

120 amps The above answer is wrong. A 60 amp breaker is designed to trip at 60 amps be it a single pole, double pole or a triple pole that is used on three phase equipment. The number on the handle of a breaker is the trip capacity.


Why would be no power in bedroom?

Blown fuse or circuit breaker. Wires loose on another outlet in that run feeding that bedroom's outlets.


How many wall outlets can you have in a circuit using a A breaker?

Assuming this is not an office of a place where lots of the outlets will be used to power items that draw lots of current on a 15 amp circuit wired with 14/2 wire I would limit it to no more than 10 outlets and lights combined. On a 20 amp circuit wired with 12/2 wire I would limit it to a 14 outlets and lights combined. There is no limit in the code. You just use common sense based on what is going to be used on this circuit.


What would cause a circuit breaker heating element to trip off?

There are two conditions that would cause a breaker to trip off. One is an overload of the circuit and the other is a short circuit on the circuit. The heating element within the breaker is what monitors for circuit overloads.


What would cause a short periodic low hum to come from a circuit breaker?

A bad circuit breaker. Replace it.


How many outlets are allowed on a 240 v branch circuit?

Branch circuit loading In Canada the CEC states that there shall be not more than 12 outlets on any 2-wire branch circuit. These outlets shall be considered to be rated at not less than 1 amp per outlet Where the connected load is known, the number of outlets shall be permitted to exceed 12, provided that the load current does not exceed 80% of the rating of the over current device protecting the circuit. For example on a 15 amp breaker, 15 x 80% = 12 amps, hence the standard of 12 outlets on any 2-wire branch circuit. On a 20 amp breaker, 20 x 80% = 16 amps. So from a 20 amp breaker this allows 16 outlets on a 2-wire branch circuit as long as the outlets are not considered to be rated at less than 1 amp per outlet. The definition of an outlet is a point in the wiring installation at which current is taken to supply utilization equipment. What this means is that if a light switch and a fixture outlet were on the same 2-wire branch circuit they would be subtracted from the maximum count of 12 receptacle outlets on the circuit which would leave 10. If the light fixture draws 3 amps plus the switch outlet, then the total circuit outlet count would be reduced to 8 receptacle outlets (12 -- 3 -- 1 = 8). On a standard specification home most electricians will wire one circuit per room, the outlet count usually never reaches the maximum of 12 outlets.


What would happenif you put an 8 amp circuit-breaker in a power circuit?

The circuit would be protected up to 8 amps before the breaker would trip. Any more that 8 amps and the circuit would open and shut the circuit off.


What if your circuit breaker started tripping with no change of things plugged into an outlet Does this mean the circuit breaker needs to be replaced?

Circuit breakers can degrade over time but it would be better to get a competant electrician to do it. It might also mean you have too many things plugged into one outlet. Sometimes one circuit breaker may protect several outlets so it might be tripping because of a change in another outlet. ELECTRICTY IS DANGEROUS!!!! Don't do it yourself.


What is an example of a circuit interrupter?

An example of a circuit interrupter would a fuse or circuit breaker.


How many oulets in a 15 amp breaker circuit?

Branch circuit loading In Canada the CEC states that there shall be not more than 12 outlets on any 2-wire branch circuit. These outlets shall be considered to be rated at not less than 1 amp per outletWhere the connected load is known, the number of outlets shall be permitted to exceed 12, provided that the load current does not exceed 80% of the rating of the over current device protecting the circuit. For example on a 15 amp breaker, 15 x 80% = 12 amps, hence the standard of 12 outlets on any 2-wire branch circuit.On a 20 amp breaker, 20 x 80% = 16 amps. So from a 20 amp breaker this allows 16 outlets on a 2-wire branch circuit as long as the outlets are not considered to be rated at less than 1 amp per outlet.The definition of an outlet is a point in the wiring installation at which current is taken to supply utilisation equipment. What this means is that if a light switch and a fixture outlet were on the same 2-wire branch circuit they would be subtracted from the maximum count of 12 receptacle outlets on the circuit which would leave 10.If the light fixture draws 3 amps plus the switch outlet, then the total circuit outlet count would be reduced to 8 receptacle outlets (12 &ndash; 3 &ndash; 1 = 8).On a standard specification home most electricians will wire one circuit per room, the outlet count usually never reaches the maximum of 12 outlets.


What would cause a 20A circuit breaker to remain on but have power with only two outlets and nothing anywhere else?

A disconnected or broken wire along the path somewhere. If you have 5 outlets (in a row) on a breaker and the wire breaks at the 3rd outlet, the first two outlets will still work but the others will not. Rodents are known to gnaw on wires and that can cause the break. Or maybe a wire just came loose from a recepticle.