No. In North America a double pole breaker is used to obtain a voltage of 240 volts from the distribution panel. What ever the amperage rating stamped on the handle of the breaker is, that is the amperage that the breaker will trip at.

User Avatar

Wiki User

โˆ™ 2014-07-26 03:27:40
This answer is:
๐Ÿ™
0
๐Ÿคจ
0
๐Ÿ˜ฎ
0
User Avatar
Study guides

๐Ÿ““
Create a Study Guide

Add your answer:

Earn +20 pts
Q: Does a double pole breaker double the amperage?
Write your answer...
Submit
Related questions

Does a double 50 amp breaker make a 100 amp?

No, a double pole 50 amp breaker protects a 240 volt supply at 50 amps. The number that is on the handle of the breaker is the amperage that the breaker will trip at if an overload occurs on the circuit.


What amperage is a dual 60 amp breaker?

120 amps The above answer is wrong. A 60 amp breaker is designed to trip at 60 amps be it a single pole, double pole or a triple pole that is used on three phase equipment. The number on the handle of a breaker is the trip capacity.


What is the difference between a single pole breaker and a double pole breaker?

A single pole breaker is made or used to protect the panel buss for 110 volt devices, A double pole breaker protects the buss for 220 volt devices.


Should you buy double pole breaker or single pole?

Use of a double pole breaker or a single pole breaker depends entirely on the application. If you don't know about the application, contact a qualified electrician in your area.


How many pole breaker for air condition?

If the power requirement is 120 volts it will be connected to a single pole breaker rated at the amperage requirement of the air conditioner. If the voltage of the air conditioner is 240 volts, then a two pole breaker will be required.


Can a double pole 30 amp breaker be used as a 15 amp single pole breaker?

No, it is a 30 amp breaker on each side. Remove it and install a 15 amp single pole breaker.


Can a 220 VAC breaker be single pole or does it have to always be a double pole breaker?

U.S. 240 VAC breakers are always double pole since they are protecting two legs of the circuit.


Can you use a 25 amp double pole breaker for a 240 heavy duty whirlpool dryer.?

The recommended breaker for dryers is 30 amps. If you want to do the calculation to see if a 25 amp breaker will work use the following formula. W = A x V, A = W/V. Find the wattage of the unit and divide it by 240 volts to get the amperage. If the amperage is under 25 amps then the breaker will work. If the amperage is over 25 amps then a 30 amp breaker on #10 wire will be needed.


Can a double pole 20 amp breaker be used with 12-2 wire for a single 220 circuit?

The term "double pole" usually means a breaker with 2 handles that attaches in the space as a normal single pole breaker. If this is what you mean, no, you cannot. There is no potential, or voltage, between the wire terminals. If by "double pole" you mean what is usually called a 2-pole breaker, which is a breaker with 2 handles that attaches in the space of 2 single pole breakers, then yes, you can use this breaker and 12/2 wire to produce a 220v circuit.


Is a 2 pole 30 amp circuit breaker equivalent to two single pole 15 amp circuit breakers?

No, the number on the handle of the breaker is the maximum amount of amperage the breaker will handle before it trips. A two pole breaker is handling 240 volts. A single pole breaker handles 120 volts. Each of the "hot" wires from the two pole breaker has a potential of 120 volts to the neutral wire, but 240 volts from one "hot" wire to the other "hot" wire.


Is a double throw 15amp breaker the same as a 30 amp breaker amp?

You have a double pole breaker for 240Volt supply. The maximum current is 15 amp.


Can a double pole circuit breaker be used for 2 different circuits I have a 20 amp double pole breaker want 2 circuits running 14 gauge wire?

can a 20 amp double pole circuit breaker be used for 2 different 120 v circuits using 14 - 2 wire


Where is the double-pole circuit breaker located?

before the load


How do you change a double pole 240v breaker to a single pole 120v breaker to allow a regular 120v receptacle to work?

See Discussion Page


When going from 1-240v to 2-120v circuits do you need to replace the double pole breaker?

Yes, otherwise your double pole breaker will shut the other circuit off when one of them trips.


How do you define a pole in circuit breaker?

A pole In a circut breaker refers to the number of circuts it controls, single pole only controls one, double controls 2 at same time


What size breaker do you need for a dryer?

Usually a double pole 30 amp breaker for and electric dryer.


What is a 15 amp double pole breaker?

A double pole breaker has one pole attached to one side of your breaker panel's bus or hot leg, and another pole attached to another hot leg or bus, if it is in a residential panel (in the US) each leg of the breaker is 120 volts to ground or neutral and 240 hot leg to hot leg. The 15 amp indicates that the breaker will trip if the circuit exceeds 15 amps across the two outputs of the breaker.


How do you tell a single pole breaker from a double pole breaker?

A single pole breaker will take up one single slot in a household distribution panel. A two pole breaker will take up two slots in the distribution panel. Older double pole breaker installations had two breakers side by side with the two switch handles physically tied together. Today two pole breakers are one unit containing two output terminals for the output circuit. This new configuration has only one handle to operate both sides of the breaker for shutting the circuit off and resetting a tripped breaker.


Can a double pole 15 amp breaker help?

Help what? A double pole breaker is usually for 220/240 volt applications, but can be used for two 110/120 volt circuits. Also would depend if it is single or double throw.


What is the difference between single pole mcb and double pole mcb?

A single pole circuit breaker can protect one hot wire to a given load where as a two pole circuit breaker can protect two hot wires to a given load. In the North American system this would equate to 120 volts on a single pole circuit breaker and 240 volts on a two pole circuit breaker.


Will cobwebs trip a breaker?

No, a breaker is an amperage activated device.


What is the size breaker per phase 200kva generator?

A breaker is not sized by individual phase amperage. It will be a three phase or three pole breaker rated at the output of the generator. Use the following formula to find the output amperage of the three phase generator. Amps = kva x 1000/1.73 x voltage.


What is the amperage for a clothes dryer?

A clothes dryer is fed from a 2 pole 30 amp breaker using 3 conductor #10 wire.


How do you get 240 volts single phase from the panel?

you use a double pole breaker.

People also asked

Can a 100 amp main have 2 50 amp breakers?

View results