Best Answer

The difference between Absolute Presure and Gauge Pressure is 14.7psi. So zero gauge pressure (0psig) = 14.7 psia. 600 psig = 614.7 psia. Calibrate the tranmitter so 4mA is obtained at 14.7 psig and 20mA is obtained at 614.7psig. The span will be 600 psi in both cases.

User Avatar

Wiki User

16y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How do you calibrate PSIA transmitter. use 14.7 and the range is ATM to 600 PSIA. What would the 4-20mA set points be.?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How do you calibrate a digital oral thermometer?

One should have a standard certified temperature calibrator system before attempting to calibrate a temp. transmitter. I believe you want to calibrate the temperature sensor connected to a transmitter and to an indicator. There are three things in all. Temp. sensor it could be RTD or TC. Temp transmitter which transmits the sensor input to the indicator on which one can read the temperature. All three can be calibrated separately or together. If together it can be called loop check. Now to calibrate the transmitter know the range the transmitter and the output signal it is designed for. Say it is designed for 4-20 mAmp signal output and the range is 50'C to 200'C. It means the transmitter is supposed to give 4 ma output when it is measuring 50 'C and 20 ma when it is measuring 200 'C and be liner through out the range. Connect the transmitter to standard 4-20 ma meter. connect the standard resistance equivalent of 50'C in steps of 50'C. Measure the map signal with each step of 50'C equivalent of resistance connected. with increase in step the mamp must increase correspondingly linearly upto 200'C on the meter. Repeat the same in decreasing order in steps from 200'c to 50'C and measure the mamp. Adjust the potentiometer if any on the transmitter in case of deviation. Let the transmitter be with in its defined permissible error range while adjusting the transmitter


What is the Meaning of turn down ratio on a pressure transmitter?

This is a number that indicates what range the transmitter will work correctly. This will depend on how strong the transmitter is.


What is range of rf transmitter and receiver?

depends on frequency and power


How do you select the range for the DP level transmitter?

BY Product Specification


Can I buy a cable to extend the range of my wireless mouse's transmitter?

There is not a cable that can extend the range of a wireless mouse.


What is the transmitting range of 10kw FM transmitter?

As FM is transmitted using VHF, the transmitting range is more a matter of Line of Sight than transmitter power as these frequencies only follow straight lines.


What does the jammer in black ops do?

Disables enemies radars within the range of the transmitter.


What is the range of the balance weight set class c used to calibrate tensiometers?

rack and pinion assembly


What is the frequency band alloted for a long-range FM transmitter?

From 88.5 to 107.9 MHz


Transmitter concentrates the signal energy at a single frequency or in a very small range of frequencies?

narrowband


A transmitter concentrates the signal energy at a single frequency or in a very small range of frequencies?

narrowband


How do you create transmitter?

we can create transmitter by using modulator circuit depending what frequency range you would like to use if you want to use FM range 88 to 108 MHz than you may refer to FM modulators and if you are going to more than 300MHz than you will need RF receiver.