For dwellings, per NEC, convenience outlets are included in the general lighting load calcs, figured at 3VA per square foot, measured to the outside walls. For other occupancies, each receptacle is figured at 180VA.

User Avatar

Wiki User

15y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How many volt amps for typical convenience outlet design?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How many amps in standard 110 outlet?

15 amps


How many amps does a small microwave use?

13 amps should be a dedicated outlet since one outlet has a maximum capacity of 15 amps <<>> If the supply voltage is 120 volts then the amperage is I = W/E. Amps = Watts/Volts = 1450/120 = 12.08 amps.


What is the amperage of a standard power outlet in China?

10 amps 250 volts or 16 amps 250 volts.


How many watts can you get from a wall socket in a house?

This can vary. In the United States a wall socket/outlet is usually limited to 15 amps (amperes) at 120 volts.Watts = Volts x Amps, so120 x 15 = 1800The typical US wall outlet can deliver 1800 wattsSome outlets are wired for 20 amps in which case they support 2400 watts.NOTE: It can be more complicated than this depending on what's plugged into the outlet. A motor (like in a vacuum cleaner or refrigeratior, etc.) can take amps in that it sends back out without using. Thus, it uses less watts than the amps that flow through it. In this case since the outlet is limited by amps the watts it can deliver to such a device is less than 1800 watts.Answer for the UKUK sockets are rated at 13 A at 230 V, so are capable of (13 x 230 = 2990 W) in nominal terms, or 3 kW in practise.


Why do you need 20 AMP power outlet?

To apply power to a load greater that 15 amps and smaller than 30 amps.


How do you confirm that you are not overloading an outlet?

Check the number of amps that your circuit can handle. You should not put devices with more than that many amps (total) on that circuit. Most houses are 15 amps and bathrooms 20 amps.


How much amperage can a typical thermostat handle?

2 amps


Does one outlet in a house carry more amperage than another outlet?

Usually no. In the regular home, outlets give out the same amount of power. Every outlet does have limitations. Most outlets can handle up to 15 Amps, however outlets in the garage or outdoors usually handle 20 amps.


What is the Difference between a 3057K and 4057K bulb?

3057K - Design AMPS: 2.1, Rated Life: 2,000 4057K - Design AMPS:2.23, Rated Life: 4,000


What is the typical amp draw on a low voltage circuit?

2 amps


What is alternating current through 100 Watt bulb connected at wall outlet?

The current is 0.83 amps on 120 v or 0.42 amps on 240 v.


What happens if i plug a 25 amps machine to a 30 amps outlet?

Plugging a lower drain machine into a higher drain outlet is perfectly fine, the outlet will be able to deliver all that the machine needs. And the machine will only use up what it needs, so having excess at the outlet isn't going to hurt anything. The other way around, a machine pulling more than the outlet can deliver, will trip the breaker or blow the fuse.