7200 Watts, but that is only the trip value of the breaker. The circuit should only sustain 80% of the rated load, so a 240 volt 30 amp circuit can carry 5760 watts.
answer 2 Both a circuit breaker and a fusible link are current operated, not wattage operated. So 7200 watts is the answer to the stated question. But the correct answer is 30A.
HOWEVER if it is not a CB or fuse, but an electrical outlet that is concerned, then you should not overload the outlet (wall socket). If it says 30 Amp, then that's it.
Similarly if it is a cable or wiring that is being inquired about. The 240 volt refers to the insulation value of the cable, the 30 Amp refers to the current carrying capacity of the conductor.
The question is not perfectly clear.
i have a 4800 watt heater that's 240 volts. What size breaker is needed?
240V x 30A = 7.2kW
or the more general formula:
Volts X Amps = Watts
Depends on the voltage. Watts = volts x Amps
On 110 volts = 3300 watts.
The formula you are looking for is W = I x E. Watts = Amps x Volts.
3600 watts when part of a 120 v circuit. Multiply voltage times the amperage to get watts.
220 x 30 = 6600 Watts
7200 W.
2304w
Not a whole lot. Assuming that is 120 volt power, 1200 watts would be 10 amps. A standard breaker is 15 amps.
2.3 kw per hour on a 110-120 volt circuit.
One volt is zero watts.
Not sure about how many Watts your 36 volt charger uses, but you can find out by this formula... Volts X Amps = Watts.
2304w
Not a whole lot. Assuming that is 120 volt power, 1200 watts would be 10 amps. A standard breaker is 15 amps.
2.3 kw per hour on a 110-120 volt circuit.
One volt is zero watts.
Not sure about how many Watts your 36 volt charger uses, but you can find out by this formula... Volts X Amps = Watts.
The load exceeds the limit of the breaker or fuse. For example a 20 amp breaker on a 120 volt circuit will handle 2400 watts. Exceed that wattage and the breaker will trip or the fuse will blow.
Volts * Amps = Watts 12 Volt * 2 amp = 24 Watts
On a 120 volt supply, up to 360 watts. On a 240 volt supply, up to 720 watts.
770 watts.
20-amp breakers can be found for many different voltage levels. The higher-voltage ones tend to be more expensive. A breaker can be used in a circuit of equal or lower voltage than the rated voltage of the breaker.
It's the amps that are controlled by the breaker not the volts. You can have a 600 volt 15 amp breaker, you can have a 347 volt 15 amp breaker. The breaker will trip when you exceed 15 AMPS.
750 watts per horse power20 x 750 = 15,000 watts / 220V = 68A68 amps at 220 volts