Best Answer

The usual allowable voltage drop is 5%, or 6 volts on a 120 v supply. For a 50 amp supply that means the total wire resistance must be (at most) 6/50 ohms, or 0.12 ohms. Because there is 300 ft of wire the resistance per ft must be 0.12/300 ohms per ft, or .0004 ohms/ft or 0.4 ohms per 1000 ft. Wire tables show that #6 AWG wire is needed, with a cross-section area of 13.3 sq mm.

<<>>

Answer for USA, Canada and countries running a 60 Hz supply service.

The code book suggest that a 3% voltage drop should be the maximum allowed. A #3 copper conductor will limit the voltage drop to3% or less when supplying 50 amps for 150 feet on a 120 volt system.

User Avatar

Wiki User

βˆ™ 10y ago
This answer is:
User Avatar
User Avatar

Anonymous

Lvl 1
βˆ™ 3y ago
Thank you very helpfulΒ 
More answers
User Avatar

Wiki User

βˆ™ 11y ago

If it's a 50-amp panel designed for 100 percent full-time load at 120 volts, you would plug those numbers into a voltage-drop calculator and it will tell you.

A #3 AWG copper conductor pair in conduit, overhead or direct burial will give you 85 Amps with only about 3.6 volts (3 percent) voltage drop.

#4 AWG would give you 4 percent drop (at max current).

#6 AWG would give 6 percent drop, but only 3.6 percent at 30 Amps.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 14y ago

min of # 6 thhn copper

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What size wire do you need for 50 amp sub panel about 150 feet away 120 volts?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What size wire do you need to run overhead to a 50 amp service five hundred feet away?

For that distance I would run AWG # 3 copper and install a sub-panel.


What gauge wire would I need for 2500 feet for 240 volts and 0.4 amps?

A #14 wire will do the job.


Can you use a 0.4w 4.5v solar panel to charge a 4.8v battery?

Most likely not. In order to charge the battery to its nominal rated 4.8 volts, youreally need a source capable of more than 4.8 volts open-circuit.You need to take the solar panel and a voltmeter, and measure the output voltageof the solar panel with no load connected to it. If it's more than 4.8 volts, then itwill charge your battery.But . . .That's not saying anything about how long it will take. 0.4 watt is not an awful lotof power, and your solar panel will not even deliver that much before its outputvoltage sags to 4.8 . So I would think that this solar panel will not be an acceptablecharger for that battery.


How do you remove the door panel of a 1995 k2500 Chevrolet Suburban?

To remove the door panel you will need to find and remove all screws. Once you have taken out the screws you will need to gently pull the panel away from the door.


Can a 240 volt sub panel run 115 volt motor?

In Europe 240 volts is standard, so no a 115 volt motor will not work. In USA 120 volts is standard, so if your sub-panel has 120 volts, (check with voltage meter) then yes. Read carefully, To get 240 volts in a sub-panel in USA the electric company brings two (2) wires, each wire has 120 volts, 120 + 120 = 240. One of those 120 volts will run your motor. Look for the wires from the electric company and check them with your voltage meter. If this is a commercial application you will need to call an electrical contractor, power companies for commercial applications do not follow the above.


How many feet away do you need to be parked away from a stop sign in your neighborhood?

school busses have a bumper sticker which reads "keep back 100 feet". i do not know about city busses


How close do you need to hear an elephant rumble?

10 feet away


What size wire do you need to carry nineteen amps for two hundred feet at two hundred forty volts ac?

10 guage


If you have double vision within 2 feet do you need eyeglasses?

Yes, you need eyeglasses if you have double vision within up to 20 feet away.


What circuit breaker to install for 10 amp 250 volt circuit?

You need a breaker rated for 10 amps and 250 volts. The breaker must also fit properly in your panel.


How to increase 115 volts to 220 volts?

You need a step-up transformer.


How many watts of electric on a 13 amp fuse 240 volts?

You need the formula: Amps * Volts = Watts But you get to do the math.