It depends on what 277 volt device you are trying to connect.
That's 277 volts of alternating current. This is typically one phase of a 480v 3 phase system. Don't worry that 3 x 277 adds up to more than 480v. A 277v line is typically one phase of a 480v 3 phase system.
If there is no ground wire connect the ground wire to the neutral wire.
R - Red Y - Yellow B - Blue
The neutral wire and power wire are never connected together.
Wire size is governed by amperage not voltage. Voltage is an insulation factor when talking about wire. Add up the amperage of fixtures you want in the circuit. Once that is found then the size of the wire can be calculated.
Should be about 120 VAC.
If you are talking about a 4-wire branch circuit you'll need to start with a 220 VAC breaker. It will have two terminals. Connect black and red wires to the two terminals. Doesn't matter in which order you make this connection. The white wire goes to the neutral bus bar where all other white wires are connected. The green or bare wire goes to ground bus where other bare wires are connected.
wire is often rated at 600 vac, 22 amps reqires # 10
It seems like you are describing the Red, Black, White and Ground in your electric panel. There is 240 VAC between Black and Red and 120 VAC between Black and White and 120 VAC between Red and White. The electric panel has two busses that supply 120 VAC on alternating breakers in your panel. Essentially, the Red turns into "black" in the panel for all practical purposes. If you have a 240 VAC circuit it essentially takes up to two vertical positions in your electric panel.
That is all that is needed to wire the fixture. The 277 volts is the line to neutral of a 480 volt three phase system. Any one of L1, L2 or L3 to the neutral will give you the 277 volts that you need to connect the fixture so that it will operate.
In WYE 480 VAC each leg to neutral is equal to 277 volts. 480 / 1.73 (sq root of 3) = 277.
White is the neutral wire. Black is hot, green is ground.
how do you connect the wire from the alternater to the starter?
Use a small light bulb, such as 25-50 watt. Connect 120 VAC power to the big L1 terminal. Connect the big T1 terminal to the light bulb. Connect the neutral to the light bulb. The light bulb will be OFF. Connect another 120 VAC wire to the control input terminal #3. Connect another neutral to the control input terminal #4. The light bulb will now be ON. See the drawing at the bottom of: http://www.power-io.com/products/dda5075100.htm
no
Yes.
Connect the sub woofer to the equalizer or amplifier. The positive wire will need to be connected to a power source. Connect the ground wire. Connect the auxiliary wire to the amplifier.