you get a transformer...

User Avatar

Wiki User

16y ago

What else can I help you with?

Related Questions

How many amps in 120volts and 500ohms?

You use Ohm's Law to make your calculation. Volts = Amps x Resistance Amps = Volts / Resistance


How many amps make a Kw?

Depends on the voltage. Watts are volts x amps.


I want to convert 12 volts DC to 29.5 volts DC by using a 400 watt power inverter will it work?

In short, no. There are ways to make the voltage rise, but inverting the power will not help you. If you don't care about the amount of Amps you have, the simplest way to raise the voltage would be to add resistance to the line. Volts and amps are linked by Ohm's law, which states that V=IR, where V is volts, I is current (in amps), and R is resistance in ohms. Therefore you can create a higher voltage at the cost of amperage by adding resistance to your line.


How do you make a 6 volt battery into a 12 volts?

That is Impossible. You can however make two 6 volt batteries into a 12 volt system by wiring the two 6 volts batteries in Series. You will then have an output voltage of 12 volts but the amperes will only be what one of the batteries have, In other words the volts will double but the amps will stay the same as if you only had 1 battery connected.


How many volts does it take to make 1 horsepower?

Volts don't make power. Watts do. Watts = (volts) x (amps) 1 horsepower = 746 watts


How many amp in 10 HP?

How to convert horsepower to amps? You'd have to make an assumption about volts. If it's running at 220 volts, that would make it 34 Amps. There are 746 watts in a horsepower and Amps = Watts/Volts.


How much current would a 5-kW heater draw with 230 volts?

The formula you are looking for is I = W/E, Amps = Watts/Volts. Amps = 5000/230 =21.7 amps. The wire size to run this heater would be a #10 copper conductor. The supply breaker would be a two pole 30 amp breaker.


How many kw does it take to make 100 amps?

If the 100 amps is powered by 10 volts, you have 1 kw, or 1000 watts. watts = volts X current The 'k' simply means kilo, or thousand.


How many amps do you need to supply a 150kva transformer to get 118amps 480 volts?

Rephrase your question, as it doesn't make any sense. If the primary side of the transformer is 480 volts 3 phase, this transformer can be supplied from a breaker as big as 180 amps. If 480 volts 3 phase is your secondary then you can supply up to 180 amps to your loads.


Is it a problem to use an adaptor with an output of 4.74 amps and 19 volts when the Laptop's input is 3.42 amps and 19 volts?

No problem whatsoever. As long as Voltage is the same and the supply Amps is greater than the laptop's Amps, all will be well. The Voltage will be supplied no matter what your laptop needs, creating an overload if the supply is greater than the demand. The Amperage will vary automatically depending on your laptop's need. There would be a problem if you used a 19V 2A power supply.


How many dc volts does it take to make 1 horsepower?

Volts don't make power. Watts do. Watts = (volts) x (amps) 1 horsepower = 746 watts (Doesn't matter if the source is AC, DC, or a combination of both.)


How many volts will it take to make 12 amps go through 3 ohms of resistance?

Use Ohm's Law: V = IR (voltage = current times resistance).