Answer for USA and Canada power supply service. Presuming a "15 amp circuit" is meant as a 120 volt system with a 15 amp single pole breaker with #14 awg wire, then: Per the National Electric Code, a breaker can only be loaded to 80% of rating. Thus, a 15 amp breaker can only feed a 12 amp max load. If the loads that will be plugged into the receptacles are unknown, then 180 watts shall be used for each duplex receptacle. Maximum load allowed on the breaker is 120 x 12 = 1440 watts. Maximum receptacles allowed on circuit is 1440 / 180 = 8. Still, read the NEC or other required codes depending on the installation location and connected equipment. In Canada, there shall be not more that 12 outlets on any 2 wire branch circuit. Such outlets shall be considered to be rated at not more that 1 amp per outlet. Where the connected load is known, the number of outlets may exceed 12 providing the load current does not exceed 80 % of the rating of the over current device protecting the circuit.

User Avatar

Wiki User

14y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

14y ago

By code, ten is the maximum number. Each receptacle is rated at 180 VA (volt-amps). Nominal voltage per code is 115V. And circuits are not to be loaded more than 80%. Therefore 20A X 115V = 2300 VA divided by 180VA = 12.7 X .8 = 10 (10.16)

This answer is:
User Avatar

User Avatar

Wiki User

12y ago

Depends on requirements of applicable electrical code or specifications, and where receptacles are located. For instance, all of the receptacles on a particular circuit could be GFI as GFI protects the load side of the receptacle,

This answer is:
User Avatar

User Avatar

Wiki User

11y ago

It depends upon what the circuit will be used for. Some uses would only allow a single receptacle, such as one intended for a portable 1500-watt heater.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How many receptacales on 20 amp circuit?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How many elec outlets can a GFCI detect?

7 on a 15 amp circuit and 9 on a 20 amp circuit.


New shop 20 amp circuit 32 amp fixture how many fixtures can be put on circuit?

A 32 amp fixture can not be fed from a 20 amp breaker as the breaker will trip every time.


How many 1.2 amp lights can a 20 amp breaker hold?

No more than 13 maximum on a 20 amp circuit.


How many amps equal 1 circuit?

80% of the rated circuit. 10 amp circuit is 8 amps, 20 amp circuit is 16 amps, etc.


What circuit is a microwave?

A dedicated 20 Amp circuit wired with 12/2 wiring an a 20 amp breaker.


How many outlets are there?

Up to 12 on a 20 amp circuit. Up to 9 on a 15 amp circuit. But use common sense. If the circuit will be heavily loaded, as in a home office, then do not install that many.


What can a 20 amp circuit be used for?

A 20 amp circuit be used for any device that takes up to 20 amps to make it operate.


How many outlets can run off 1 gfi outlet?

Eight on a 15 amp circuit, tweleve on a 20 amp circuit, including the gfci receptacle itself.


How many lights on 20 amp circuit?

Provided you use wire that is rated for 20 amps.


Can you use an 18 amp appliance on a 20 amp circuit?

Yes, if properly wired a 20 amp circuit is a great circuit for an 18 amp appliance. Properly wired means you've used 12 gauge wire or larger and the circuit is protected by a 20 amp breaker or fuse and all connections are secure.


What amp plug does the average router have?

15 amp outlet on a 20 amp circuit.


Can you control 10 outlets with one 20 amp GFCI outlet on one 20 amp circuit?

Yes. I know of no limits to how many regular receptacles (outlets) you can "piggy back" onto one GFCI receptacle. However, in commercial and industrial construction there are limits to how many receptacles can be placed on any one circuit. These limits in the United States and according to the NEC are: 10 receptacles on a 15 amp circuit and 13 receptacles on a 20 amp circuit.