The maximum wattage that a 30 amp breaker can handle is 30 x 230 = 6900 watts. Other variables come into play and this number will decrease depending on the load, duty time, and difference in voltage fluctuation.
The connected load in watts to a single pole 30 amp breaker is calculated by the following equation. W = I x E. Watts = Amps x Volts. A higher wattage than what you calculate will trip the breaker.
Also another equation you should be familiar with, for breaker sizing if only the wattage is given on the nameplate, is that for amperage from watts. I = W/E. Amps = Watts/ Volts.
14 gauge will handle it with a 15 amp breaker. If you use 12 gauge use a 20 amp breaker.
Yes, in home wiring as long as it is protected by a 15 amp breaker. Remember this circuit will only handle 1800 watts and cannot be loaded to any more than 1440 watts. So if each light is 75 watts then the maximum you can install is 19.
What governs the type of breaker is the voltage and wattage of the heater elements. If the tank is 120V then you would only use one breaker. The size of the breaker you use will depend on the watts of the element. Watts = amps x volts, Amps = Watts/ volts. Once you establish the amperage then size the wire and the breaker to fit. If the tank is 240V the same rules apply only you would use a 2 pole breaker. IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOBSAFELY AND COMPETENTLYREFER THIS WORK TO QUALIFIED PROFESSIONALS. If you do this work yourself, always turn off the power at the breaker box/fuse panel BEFORE you attempt to do any work AND always use a meter or voltage indicatorto insure the circuit is, in fact, de-energized.
No. 20 amps at 120 volts will handle a maximum of 2400 watts. And you should never continuously load a 20 amp 120 volt circuit to no more than 1920 watts.
Breaker sizing is dependant on what the load amperage is that the breaker is connected to. If the amperage is not given but just the wattage, use this equation I = W/E. Amps = Watts/Volts. This air conditioner unit should be on a dedicated circuit receptacle. On these types of loads the conductor can only be loaded to 80% of the conductors rating. So a 15 amp breaker times 80% = 12 amps or Watts = Amps x Volts, 12 x 120 = 1440 watts. A 20 amp breaker times 80% = 16 amps or Watts = Amps x Volts, 16 x 120 = 1920. Once the breaker is sized remember to use the correct wire size to correspond with the amperage of the breaker.
Watts = Amps x Volts. 60 x 240 = 14400
30X240=7200
Answer for the US: Breakers are rated in amps, not watts. However, a 15A breaker can handle 15 amps, or about 1800 watts (using 120V), or 3600 watts (using 240V). However, this is only rated for noncontinuous loads (those not lasting for more than three hours). For continuous loads (loads lasting three hours or more), one must derate the circuit breaker by 80%. So for continuous loads, that same breaker should only have 1440 watts (using 120V), or 2880 watts (using 240V) on it.
14 gauge will handle it with a 15 amp breaker. If you use 12 gauge use a 20 amp breaker.
A 15 amp switch can safely handle up to 1400 resistive watts.
2.3 kw per hour on a 110-120 volt circuit.
Wattage (power) is not stored in a breaker; in its tripped position, electrical power form the power line is disconnected. When the breaker is activated, electricity (power) flows through the breaker to the circuit in the home. Using the formula below, you can find the wattage the breaker can handle, not how much it has. Watts = Volts x Amps = 120 volts x 15 amps = 1800 watts A toaster requires 1500 watts of power, so if you are running a coffee maker which probably requires 700 watts or more and turn on you toaster, that 15 amp breaker will trip.
The load exceeds the limit of the breaker or fuse. For example a 20 amp breaker on a 120 volt circuit will handle 2400 watts. Exceed that wattage and the breaker will trip or the fuse will blow.
Lamps with five flexable lights that provide great lighting and come with shades and four way switches. The information below is telling you how brite the light will be if you used the same number watts in the lamp. Using 15 watt bulbs Using 30 watt bulbs Using 40 watt bulbs Using 60 watt bulb Switch 1: 30 watts Switch 1: 60 watts Switch 1: 80 watts Switch 1: 120 watts Switch 2: 45 watts Switch 2: 90 watts Switch 2: 120 watts Switch 2: 180 watts Switch 3: 75 watts Switch 3: 150 watts Switch 3: 200 watts Switch 3: 300 watts Switch 4: 0 watts Switch 4: 0 watts Switch 4: 0 watts Switch 4: 0 watts
The formulae for calculating watts to amps is Watts divided by Voltage. Therefore to get from Amps to Watts the calculation is Amps × Voltage. Therefore if you are working on a 240 volt supply the calculation is 20 (Amps) × 240 (Volts) which = 4800 watts.
At 120 volts a 15 amp breaker can be loaded to 1800 watts before it will trip. If it is a continuous load then the electrical code states that it is only allowed to be loaded to 80%. This will be 1800 x .8 = 1440 watts. If the voltage is not 120 volts use the following equation Watts = Amps x Volts. Amps being the breaker size that is to be used.
A dimmer switch is used for lighting loads and not heating loads. The wattage rating on a dimmer switch is what the manufacturer recommends as the maximum load that the switch can handle. For example if you have ten 100 watt lamps, the total load wattage would be 1000 watts (10 x 100). Too much load for a 600 watt rated dimmer switch but not for a 1000 Watt rated dimmer switch. So you can see that the rating on a dimmer switch governs the maximum wattage load that can be connected in the circuit that is to be controlled.