Want this question answered?
Minimum size is 10 gauge with a 30 amp breaker. To be safe I would install an 8 gauge with a 40 amp breaker.
You need a 60 amp breaker.
Yes, if you are running it no farther than 100 feet. If you are going over 100 feet use AWG # 10 wire on the 20 amp breaker.
15 amps
The size of the main breaker depends on the maximum current rating of the 10 gauge wire and the load it will be powering. Typically, a 10 gauge wire is rated for a maximum current of 30 amps. Therefore, a 30 amp main breaker would be suitable for running 10 gauge wire. However, it is important to consult local electrical codes and consider the specific load requirements before making a final determination.
No, 10 gauge wire requires the use of a 30 amp breaker. A 20 amp breaker is only used on 12 gauge wire.
Minimum size is 10 gauge with a 30 amp breaker. To be safe I would install an 8 gauge with a 40 amp breaker.
If you are connecting 120 volts, you connect the black wire to the breaker, white wire to the neutral bar, and ground wire to the ground bar. If you are connecting 240 volts connect the black & white wires to the breaker, & ground wire to the ground bar.
You need a 60 amp breaker.
No. A 20 amp breaker needs 12 gauge wire.
Yes, if you are running it no farther than 100 feet. If you are going over 100 feet use AWG # 10 wire on the 20 amp breaker.
A domestic D/W uses 14 gauge wire.
Use AWG # 6 wire.
15 amps
AWG 12.
10 guage.
You listed no gauge wire. This is the required breakers.14 gauge - 15 amp12 gauge - 20 amp10 gauge - 30 amp8 gauge - 40 amp