No, it is not safe to use a #8 conductor on a 50 amp breaker. A #8 conductor is only rated at 45 amps capacity. By connecting it to a 50 amp breaker, which would trip at 50 amps on an overload, would overload the conductor by an extra 5 amps. This would be a conflict against the electrical code.

User Avatar

Wiki User

12y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: It is safe to use 8-3 wire on a 50 amp breaker?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

Is it safe to use 10 gauge wire on a 20 amp breaker for a microwave?

No, 10 gauge wire requires the use of a 30 amp breaker. A 20 amp breaker is only used on 12 gauge wire.


How big of breaker do you use for 115 volt?

Depends on the wire size used in the circuit. If you use AWG # 14 wire you must use a 15 amp breaker. If it is wired with AWG # 12 wire then you use a 20 amp breaker. If a AWG # 10 wire is used then a 30 amp breaker is required. The breaker protects the wiring from overheating so you must use the proper size breaker for the wire used.


What breaker do you use for 10 2 wire?

Use a 30 amp breaker.


Is a 12 gauge wire on 20 amp breaker safe for a sub panel?

Yes, if you are running it no farther than 100 feet. If you are going over 100 feet use AWG # 10 wire on the 20 amp breaker.


What size amp circuit breaker should be used for a home entertainment system?

You use the correct size breaker depending on the size wire in the circuit. If the circuit is wired with AWG #12 wire use a 20 amp breaker. If it is wired with AWG #14 wire then use a 15 amp breaker.


What size amp circuit breaker should be used for 110 outlet?

The size breaker you use is determined by the size wire used in the circuit. If you use AWG #12/2 wire then use a 20 amp breaker. If you use AWG # 14/2 then use a 15 amp breaker.


Should 25 amps breaker be replaced by 20 amps?

For typical residential house wiring 12 AWG wire is required for a 20 Amp breaker. If you change out the breaker for a 25 A breaker you would have to rewire the circuit with 10 AWG. In that case you could up the breaker to 30 Amps. All outlets and switches should be rated at the same voltage and current as the breaker.


Can you use 14-3 wire on a 20amp breaker?

No. A 20 amp breaker needs 12 gauge wire.


What size breaker should you use for a tnia-10 wire?

25 amp breaker


What best breaker rating for 1.5 hp air-con unit?

The breaker you use is determined by the size of the wire in the wall not by what is being connected to that circuit. If you have 14/2 wire then use a 15 amp breaker. If you have 12/2 wire then use a 20 amp breaker. The breaker protects the wiring not the item connected.


What best breaker rating for 1.5 hp air con unit?

The breaker you use is determined by the size of the wire in the wall not by what is being connected to that circuit. If you have 14/2 wire then use a 15 amp breaker. If you have 12/2 wire then use a 20 amp breaker. The breaker protects the wiring not the item connected.


What size wire for 75 feet of wire for a 30 amp 220 volt oven?

A 30 amp breaker run 75 feet would require you use AWG #10 wire. But, an oven normally pulls more that 30 amps and I would not use #10 wire on a 30 amp breaker for an oven. Normally any newer oven is wired with AWG #6 gauge wire on a 50 amp circuit breaker so the breaker will not trip during heavy use of the oven. Some older ovens could use a #8 wire on a 40 amp breaker.