#4 thhn copper or # 2 aluminum
My memory says correct gauge for 100 amp service is 1 0 (that is, one ought) I could be wrong, check with your power company or building inspector.
Copper SE cable gauge 00 from the meter socket to the breaker panel for a 200A service. Then 8, 10, 12, and 14 gauge wire depending on the load.
how deep should water line be from meter to house in Versailles Kentucky
what should the volt meter guage read in my '93 Jeep Wrangler 13.5 to 14.2?
For a 200A service, the recommended copper wire gauge for service entrance cable is typically 2/0 AWG (American Wire Gauge). This wire size is able to handle the ampacity required for a 200A service safely and efficiently. It is always recommended to consult with a licensed electrician to determine the appropriate wire size for your specific installation.
The point of connection will be at the utility meter base, Whether the service is installed from a pole (overhead) or underground. In an overhead installation, the conductors may physically attach to the house at points other than the meter base, but they will always end up at the meter base.
1.676m,1.00m
1.09361
Usually the power provider will conned the wires to the transformer. If your house if fed over head, your service will attached to an insulated attachment point on the house or service mast. Then they will pass through the meter, and then into the main breaker in your electrical panel. If your house is fed underground the service wire will be burred underground and enter the electrical meter from the bottom If you can elaborate a little more I can give you a more precise answer
You do not remove the electric meter from a house. Ever. You could be electrocuted or have an explosion in front of your face, putting molten metal through you. You must call the power company and they will send a properly trained and properly safety-equipped technician to remove the meter from the house. Even the fire department is no longer authorized to "pull a meter". They would rather have your house burn down than risk the life of a firefighter making an attempt to pull the meter, even with firefighting protective equipment. Do not attempt to remove an electric meter from a house.
A pressure gauge is called a gauge because it typically measures pressure relative to atmospheric pressure, which is often considered as the reference point or zero point for pressure measurements. On the other hand, a meter usually measures absolute values without reference to a specific point.
Meter gauge tracks are one meter or 39.4 inches apart. Standard gauge rails are 4 feet 8 and one half inches apart. Broad gauge is 5 feet between the rails. Most USA railroads use standard gauge although Broad gauge was common in the American South before the Civil War. It is still common in many parts of Russia.