answersLogoWhite

0

What else can I help you with?

Continue Learning about Electrical Engineering
Related Questions

Can 120 240 volt and 277 480 volt conductors be installed in the same conduit or box?

NO! The National Electric Code requires a partitioned box when high and low voltages share the same box. Always avoid installing different voltages in the same box, it's a bad idea. <<>> A 277 volt switch has a different screw to box configuration that a 120 volt switch. This is also true for 347 volt switches. The switch is configured this way so that 120 volt switches can not be used on the wrong voltage inadvertently According to the 2008 NEC 300.3 C 1 says yes as long as all the conductors in the wiring enclosure have at least an equal insulation rating as that of the maximum circuit voltage applied.


Can a three phase circuit be installed in the same conduit or in different conduits?

The conductors of any three phase circuit must be run in the same conduit. If the circuit requires a neutral, it must also run with the conductors in the same conduit. (If they were to be run in more than one conduit or raceway, the circuit would not operate properly.)


Can multiple feeders be in same conduit?

Yes they can. If the feeders are of different sizes, then a conduit fill calculation must be made to ascertain that the conduit does not become overfilled. Cross sectional areas of the conductors are found and it is then determined what the conduit cross sectional fill will allow.


Are all universal adapters the same?

No they are not all the same. Universal adapters come in many different voltages and work in different outlets.


Is the national grid In UK the same as us?

No. The two run at completely different voltages.


Can you run different phases in the same conduit?

No, you cannot run different phases in the same conduit. In electrical systems, different phases must be kept separate to prevent interference and ensure proper functioning of the system. Mixing phases in the same conduit can lead to imbalanced loads, increased heat generation, and potential safety hazards. It is important to follow electrical codes and standards to maintain the integrity and safety of the electrical system.


Is it legal to support a conduit from another conduit of the same size?

No, the conduit has to be supported individually from a supportive structure. The spacing of the strapping is related to the size of the conduit.


What are the reasons of getting different results using different sets of multimeters and probes for the same supply voltages?

Incorrectly calibrated meters.


How are series circuits and parallel circuits the same?

They are not. They are connected differently, and the voltages and currents behave in different ways.


How are parallel circuit and series circuit the same?

They are not. They are connected differently, and the voltages and currents behave in different ways.


Can you run 110 and 220 volt circuits in the same conduit?

Yes, 120 and 240 volts can be run in the same conduit.


Use Ohm's Law and explain how 2 circuits have the same current but different resistance?

As we know V=IR, by changing the voltages in the two different circuits, we can maintain the same current even we have different resistance.