answersLogoWhite

0

No. You aren't allowed to install a device rated greater than the circuit is rated.

The 20 amp receptacle would allow you to plug in 20 amp loads (which is why it is different than a 15 amp receptacle), and plugging a 20 amp load into a 15 amp circuit would cause an overload and the 15 amp circuit breaker would trip.

ADDITION

This may still be open for discussion. According an electrician from RKO Electric, you can in fact install a 20 Amp GFCI receptacle on a 15 Amp breaker. Apparently, the breaker will trip well before the receptacle is able to pull 20 Amps of current into the line. Please see the following link from another website: http://en.allexperts.com/q/Electrical-Wiring-Home-1734/20-amp-GFCI-outlets.htm

2003 NEC Code Book says:

210-21(b)(1), p.70-42: A single receptacle on an individual branch circuit shall have an ampere rating of not less than that of the branch circuit. To me this indicates that if there's only one receptacle on the circuit, you can't have an outlet rated for less than the circuit, but it neither mentions nor prohibits oversizing the receptacle.

210-21(3), p.70-42: Where connected to a branch circuit supplying two or more receptacles or outlets, receptacle ratings shall conform to the values listed in table 210-21(b)(3)... which says: 15amp circuit, not over15amp receptacle (20amp circuit, 15 or20amp receptacle. In contrast to (b)(1) abopve, in the case of 2 or more receptacles on the same 15 or 20amp circuit, this now seems to place the restriction on the other end of the scale. Now it does limit how large the receptacle can be rated, while also setting the boundary for how small.

User Avatar

Wiki User

12y ago

What else can I help you with?

Related Questions

What size wire do you use if you are require to wire a 6-20amp 220volt outlet?

# 6 wire


Can I use a 15 amp outlet on a 20 amp circuit?

Yes, you can use a 15 amp outlet on a 20 amp circuit. The outlet's amp rating should not exceed the circuit's amp rating.


How do you wire 15amp 230v woodworking machine. 10agw or 12agw wire and type of outlet. Into a 15amp or 20amp breaker?

For a 15 amp 230V woodworking machine, you should use at least 10 AWG wire to handle the current. You can wire it into a 15 amp breaker with a suitable outlet, like a NEMA 6-15. However, if your woodworking machine has start-up surges or is a larger machine, you may want to consider using a 20 amp breaker and wire with 12 AWG to handle the load more comfortably.


Can wall outlets be on a 15amp breaker in the bedroom or do they have to be 20amp?

Wall outlets in the bedroom can be on a 15amp breaker as long as they are not part of a dedicated circuit that may have higher power demands. Typically, 15amp breakers are standard for general outlets in residential bedrooms.


Is it safe to use a 20 amp outlet on a 15 amp circuit?

No, it is not safe to use a 20 amp outlet on a 15 amp circuit as it can overload the circuit and potentially cause a fire hazard. It is important to match the outlet with the circuit's amp rating to ensure safety.


Can you use a 15 amp outlet on a 20 amp circuit?

No, it is not recommended to use a 15 amp outlet on a 20 amp circuit as it may lead to potential safety hazards. It is best to match the outlet amperage with the circuit amperage for proper functionality and safety.


Is it safe to use a 15 amp outlet on a 20 amp circuit?

No, it is not safe to use a 15 amp outlet on a 20 amp circuit as it can lead to overheating and potential fire hazards. It is important to match the outlet's amp rating with the circuit's amp rating for safety reasons.


Will GFCI work properly if 240 volt split into one 3 wire 120 volt circuit?

No, a GFCI outlet is designed for use with standard 120-volt circuits. Attempting to use a GFCI outlet with a 240-volt split circuit could cause damage to the outlet, the circuit, and could present a safety hazard. It is not recommended to use a GFCI outlet in this manner.


Can you use32amp circuit for a 15amp appliance?

If it is a 32-amp circuit you can use any appliance that takes less than 32 amps. That includes a 15-amp appliance. All appliances fed from that circuit must use 32 amps or less in total.


What will happen if you plug a 20amp plug into a 15 amp outlet?

Plugging a 20amp plug into a 15 amp outlet can lead to overloading the outlet, causing it to overheat and potentially start a fire. It is important to use outlets that match the amp rating of the plug to prevent electrical hazards.


What happens if you use a 20amp fuse when the microwave oven calls for a 15amp fuse?

The fuse is there to protect the wiring in your home not the microwave. Using a larger fuse than required for the wiring causes a fire hazard. You can end up burning your home down. Use only the fuse recommended.


Can you use 2 20amp circuit breakers to protect to 40amp?

No, it is not safe to use two 20 amp circuit breakers to protect a 40 amp circuit. Circuit breakers are designed to protect the wiring in a circuit from overheating, and using a higher amperage circuit breaker than the wiring is rated for can lead to overheating and potential fire hazards. It is important to use the correct size circuit breaker for the amperage rating of the circuit.