answersLogoWhite

0


Best Answer

I assume you are hard wiring it and not plugging it in. The power coming into the GFCI outlet connects to the line side of the GFCI outlet. If you want the outdoor timer protected by the GFCI then connect the wire going to the timer to the load side of the outlet. If you do not want the timer protected then connect it to the line side. On the back of the GFCI if you look closely you will see Line & Load marked on the back.

User Avatar

Wiki User

12y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How do you wire an outdoor timer into a GFCI outlet?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

Why does a newly installed GFCI outlet show open ground on the tester?

Ground wire is loose or disconnected somewhere in that circuit.


Do you wire a gfci outlet differently?

No, except that you insert the wires into the holes on the back of the outlet. The power in connects to the LINE side of the outlet and power out connects to the LOAD side of the outlet. This is clearly marked on the back of the outlet. This will not only protect the outlet with the GFCI installed but all outlets receiving their power from that GFCI. If you do not want to protect the outlets receiving power from the outlet then connect that outgoing wire to the LINE side also. But know that only the outlet with the GFCI will be protected and all other outlets will not be GFCI protected.


Will GFCI work properly if 240 volt split into one 3 wire 120 volt circuit?

No, a GFCI outlet is designed for use with standard 120-volt circuits. Attempting to use a GFCI outlet with a 240-volt split circuit could cause damage to the outlet, the circuit, and could present a safety hazard. It is not recommended to use a GFCI outlet in this manner.


Can you back wire an outlet on a gfi circuit?

Don't know what you mean by back wire, but most GFCI outlets have a circuit to attach additional outlets that will be protected by the GFCI. Keep total load in minds.


Add new gfci from an existing switch?

To add a new GFCI outlet from an existing switch, you will need to run a new cable from the existing switch to the location where you want to install the GFCI outlet. Connect the new cable to the line side of the switch to ensure that the GFCI outlet is always powered. Make sure to follow all electrical codes and safety precautions while completing this task. If you are unsure about your ability to complete this task, it is recommended to consult a licensed electrician.


How do you wire a gfci outlet with fan switch?

To wire a GFCI outlet with a fan switch, connect the incoming power source to the LINE terminals on the GFCI outlet. Then, connect the load side of the GFCI outlet to the switch. From the switch, connect the power supply for the fan to complete the circuit. Make sure to follow the manufacturer's instructions and all local electrical codes for safety and proper installation.


Is it possible to use a GFCI outlet in place of an older two-wire outlet?

Yes, it is possible to replace an older two-wire outlet with a GFCI outlet. However, additional wiring modifications may be necessary, as GFCI outlets require a ground wire for proper operation. It is recommended to consult a licensed electrician for proper installation.


How do you install multiple GFCI receptacles?

A GFCI receptacle can extend its protection to regular receptacles connected to the output side of the GFCI. Each actual GFCI receptacle should be directly connected to a breaker in electric panel.


How do you wire one light and one GFCI and another light light and fan with two switches and one power line?

You can wire the first light and GFCI in series on one switch. For the second light and fan with two switches, use a 3-wire cable for the hot, neutral, and traveler wires between the switches. Connect the hot wire to the power source, and then branch out to each switch. Connect the light and fan to the switches separately using the switched leg of the power from each switch.


Can you remove an outlet or hard wired fixture from a circuit for troubleshooting a GFCI I that won't reset?

Yes, you can remove the outlet or fixture from the circuit to isolate the issue with the GFCI. Make sure to turn off the power to the circuit before removing the outlet or fixture. Once it's disconnected, attempt to reset the GFCI to see if it resolves the issue.


What could cause an outdoor outlet to lose power if the outlet is new and the wires are getting power and the breaker has not popped?

There could be a loose connection in the wiring somewhere between the outlet and the power source. This could be at a junction box, a wire nut, or a loose terminal screw. It is also possible that there is a fault in the outlet itself, even if it is new. A licensed electrician should be consulted to diagnose and fix the issue.


GFCI outlet outside this line feeds your two bathrooms can you install gfci outlets in these 2 bathrooms?

Yes, you can install GFCI outlets in the two bathrooms fed by the line from the GFCI outlet outside. It is a good safety practice to have GFCI protection in bathrooms to help prevent electrical shocks. Make sure to follow proper installation procedures and consult a licensed electrician if needed.