A #12 wire can carry 20 amps. Assuming the connected voltage is 120 volts the wattage will be Watts = Amps x Volts. W = 20 x 120 = 2400 watts. The circuit can legally be loaded to 80%. 2400 x 80% = 1920 watts. The maximum amount of loads that can be connected to a 20 amp #12 wire have to be added up individually but stay under 1920 watts.
Chat with our AI personalities
Wire guage is used as a measurement for the ampacity of the wire. # 14 wire is allowed 15 amp to be applied to it. Voltage is governed by the insulation factor of the wire. The three standard insulations are for 300V, 600V and 1000 volts.
You will need a 40 amp breaker using AWG # 8 wire running it a distance of no more than 50 feet.
No, 10 gauge wire requires the use of a 30 amp breaker. A 20 amp breaker is only used on 12 gauge wire.
Yes it is wired with copper 2 wire is also known as 14/2 wire is use for switches,outlets,lights. and a 15a outlet should only be on a 15a breaker the main power feed to your meter to your panel is aluminum and can take more of a load than copper. In the US, 15 amp receptacles can be installed on 20 amp circuits if there is more than one receptacle on that circuit. Copper wire can carry a larger load than aluminum wire of the same size.
You never, ever mix wire sizes within a circuit. However you can wire a 30 amp circuit using AWG # 8/3 wire, although that is overkill and AWG #10 wire is what you would normally use on a 30 amp circuit.