Assuming 120 VAC in a residence maximum watts = 15 x 120 = 1800 Watts. For a continuous load you can support 1440 watts which is 80& of maximum. You need 14 AWG gauge wire.
Chat with our AI personalities
14 gauge will handle it with a 15 amp breaker. If you use 12 gauge use a 20 amp breaker.
Yes, in home wiring as long as it is protected by a 15 amp breaker. Remember this circuit will only handle 1800 watts and cannot be loaded to any more than 1440 watts. So if each light is 75 watts then the maximum you can install is 19.
The maximum wattage that a 30 amp breaker can handle is 30 x 230 = 6900 watts. Other variables come into play and this number will decrease depending on the load, duty time, and difference in voltage fluctuation.
Wire is rated in ampacity, You can use only 80% of the rated ampacity. Voltage and amperage are inversely proportional. So at 120 volts alternating current you safely run 1800 watts ( I have added a small safety margin). At 240 volts you can run 3600 watts. I hope this has answered you question Ampsxvolts=watts watts/volts=amps
Breaker sizing is dependant on what the load amperage is that the breaker is connected to. If the amperage is not given but just the wattage, use this equation I = W/E. Amps = Watts/Volts. This air conditioner unit should be on a dedicated circuit receptacle. On these types of loads the conductor can only be loaded to 80% of the conductors rating. So a 15 amp breaker times 80% = 12 amps or Watts = Amps x Volts, 12 x 120 = 1440 watts. A 20 amp breaker times 80% = 16 amps or Watts = Amps x Volts, 16 x 120 = 1920. Once the breaker is sized remember to use the correct wire size to correspond with the amperage of the breaker.