answersLogoWhite

0


Best Answer

A sauna heating element is a resistive load. The equation that you are looking for is Amps = Watts/Volts = 8000/220 = 36 amps.

A #8 copper conductor with an insulation rating of 90 degrees C is rated at 55 amps. This will be fed with 40 amp two pole breaker.

User Avatar

Wiki User

11y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What amp breaker for a 220 volt 8000 watt sauna?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What size breaker for a 1500 watt 120 volt heater?

To calculate the breaker size for a 1500-watt 120-volt heater, use the formula: Breaker size = Power (Watts) / Volts. In this case, 1500 watts / 120 volts = 12.5 amps. Therefore, you would need a 15-amp breaker for a 1500-watt 120-volt heater to allow for a safety margin.


Can you run a 3200 watt oven on a 20 amp breaker?

a 220 volt, 3200 watt oven will draw under 15 amps, so yes a 2o amp breaker will work.


What amperage breaker to run 500 watt 240 volt heater?

To run a 500 watt 240 volt heater, you would need a 2.08 amp breaker. This can be calculated by dividing the wattage by the voltage (500W / 240V = 2.08A). You would typically round up to the nearest standard breaker size, which in this case would be a 3 amp breaker.


You are putting in a 240 volt 4000 watt heater in a room what size breaker do you need?

20 amp


What size breaker for 120 volt 2500 watt water heater?

For a 2500 watt water heater operating at 120 volts, you would need a 20 amp breaker. This ensures the breaker can handle the load without tripping.


What size breaker is needed to connect 5500 watt gas powered generator?

A 5500 watt gas powered generator typically requires a 30 amp breaker for a 240 volt connection. It is recommended to consult the manufacturer's specifications to ensure the correct breaker size for your specific generator model.


What size breaker needs to be installed for 15000 watt 240 volt heater?

A 15000 watt 240 volt heater would require a 62.5 amp circuit breaker. To accommodate this exact load, you would typically use the next standard breaker size above 62.5 amps, which is a 70 amp breaker to ensure safety and proper operation of the heater.


What size breaker for a 12 Volt 50 watt light?

For a 12 Volt 50 watt light, you would need a 4.17 Amp breaker. To calculate this, you can use the formula Power (W) = Voltage (V) x Current (A), rearranged to find Current (A) = Power (W) / Voltage (V). So, 50 watts / 12 volts = 4.17 Amps.


Where did the watt came from?

A watt is the product of amperage times voltage.


What is ampire?

Ampire. watt/volt


How many watt of 220 volt will get by convering inverter from 200 Watt 12 volt?

Probably about 180 watts, assuming 90% efficiency.


How many amps does a 8000 watt generator supply?

In order to determine the amperage supplied by an 8000 watt generator, you need to know the voltage of the generator. You can calculate the amperage by dividing the wattage by the voltage. For example, if the generator operates at 120 volts, the amperage would be 8000 watts / 120 volts = 66.67 amps.