answersLogoWhite

0

A sauna heating element is a resistive load. The equation that you are looking for is Amps = Watts/Volts = 8000/220 = 36 amps.

A #8 copper conductor with an insulation rating of 90 degrees C is rated at 55 amps. This will be fed with 40 amp two pole breaker.

User Avatar

Wiki User

12y ago

What else can I help you with?

Related Questions

What size breaker for a 1500 watt 120 volt heater?

To calculate the breaker size for a 1500-watt 120-volt heater, use the formula: Breaker size = Power (Watts) / Volts. In this case, 1500 watts / 120 volts = 12.5 amps. Therefore, you would need a 15-amp breaker for a 1500-watt 120-volt heater to allow for a safety margin.


Can you run a 3200 watt oven on a 20 amp breaker?

a 220 volt, 3200 watt oven will draw under 15 amps, so yes a 2o amp breaker will work.


What amperage breaker to run 500 watt 240 volt heater?

To run a 500 watt 240 volt heater, you would need a 2.08 amp breaker. This can be calculated by dividing the wattage by the voltage (500W / 240V = 2.08A). You would typically round up to the nearest standard breaker size, which in this case would be a 3 amp breaker.


You are putting in a 240 volt 4000 watt heater in a room what size breaker do you need?

20 amp


What size breaker for 120 volt 2500 watt water heater?

For a 2500 watt water heater operating at 120 volts, you would need a 20 amp breaker. This ensures the breaker can handle the load without tripping.


What size breaker needs to be installed for a 5500 watt 240 volt hotwater heater?

To determine the appropriate breaker size for a 5500-watt, 240-volt hot water heater, first calculate the current using the formula: Current (Amps) = Power (Watts) / Voltage (Volts). For a 5500-watt heater at 240 volts, the current is approximately 22.9 amps. It's recommended to use a breaker rated for 125% of the continuous load, so a 30-amp double-pole breaker is typically required for safe operation.


What size breaker is needed to connect 5500 watt gas powered generator?

A 5500 watt gas powered generator typically requires a 30 amp breaker for a 240 volt connection. It is recommended to consult the manufacturer's specifications to ensure the correct breaker size for your specific generator model.


How many amp breaker for a 2500 watt 120 volt 19 gallon water heater?

To determine the appropriate breaker size for a 2500-watt, 120-volt water heater, you first calculate the current using the formula: Current (Amps) = Power (Watts) / Voltage (Volts). For a 2500-watt heater at 120 volts, the current is approximately 20.83 amps. It's common practice to use a breaker rated at 125% of the continuous load, so a 25-amp breaker would be suitable for this application to ensure safe operation.


What size breaker needs to be installed for 15000 watt 240 volt heater?

A 15000 watt 240 volt heater would require a 62.5 amp circuit breaker. To accommodate this exact load, you would typically use the next standard breaker size above 62.5 amps, which is a 70 amp breaker to ensure safety and proper operation of the heater.


What size breaker for a 12 Volt 50 watt light?

For a 12 Volt 50 watt light, you would need a 4.17 Amp breaker. To calculate this, you can use the formula Power (W) = Voltage (V) x Current (A), rearranged to find Current (A) = Power (W) / Voltage (V). So, 50 watts / 12 volts = 4.17 Amps.


What size breaker for 4000 watt generator?

For a 4000-watt generator, you typically need a circuit breaker rated between 20 to 30 amps, depending on the voltage. If the generator operates at 120 volts, a 30-amp breaker would be appropriate, while for a 240-volt setup, a 20-amp breaker is often suitable. Always check the generator's manual for specific recommendations and local code requirements.


Where did the watt came from?

A watt is the product of amperage times voltage.