Best Answer

Service entrance wire should be AWG #3 copper.

User Avatar

Wiki User

10y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What size wire do you need for a 100amp braker?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What size copper wire to use for a 100amp single phase three meter service feed from the riser?

A #3 copper conductor with an insulation factor of 90 degrees C is rated at 115 amps.


What size wire do you need to wire a 200 am breaker box?

6


What size wire do you need for 440 three phase welder on an eight foot run?

The wire size depends on the amperage, not the voltage. The fact that the welder runs on 440 volts does not affect the wire size! You need to ask this question instead: What size wire do you need for a three phase welder on an eight foot run if the nameplate amps are 45A?


What size of electrical wire need to pass 50A?

Use AWG #6 wire.


What wire size for 100amp load for distance of 1000ft?

At that distance you will have a voltage drop of 81.25 volts if you use the recommended #6 wire on a 240 volt, 100 amp single phase circuit. Therefore I recommend you contact you electric utility and let them figure the voltage drop and the size wire required to safely run this distance. Using too small a wire can damage the electronics at the end of the run.


How you can produce 240 volts from a single phase 3 wire system with a nominal voltage of 120 volts?

you can use two hot wire different phases with a double pole braker .


What size wire for 100amp?

8 is the size of wire to use for grounding a 100 Amp panel. Green is color used for grounding8 is code.A #3 copper wire with an insulation rating of 75 or 90 degrees C is rated at 100 and 110 amps consecutively.


What is the wire size for a 35 amp breaker to a ac unit?

You will need to use #8 wire.


What size wire do you need to run to an air conditioner that has a maximum breaker size of 40 amps and a minimum circuit size of 25.3 amps?

You would need to use a wire size that is rated for at least 40 amps to be safe and to meet the requirements of the air conditioner. A common wire size for this application would be 8 AWG copper wire, which is rated for 40 amps.


What size wire do i need for a 16500 btu marine ac?

Wire size is based on the amperage of the connected load. Without that amperage an answer can not be given.


What size wire do you need for a 30 watt mixer?

For a 30 watt mixer, you would typically need a wire size of at least 18 AWG (American Wire Gauge) for power cords and connections. This wire size can safely handle the current draw of a 30 watt device without overheating. It's always recommended to check the manufacturer's specifications for the mixer to ensure you are using the correct wire size.


What wire size for 400 amp service neutral size?

You need to look at the regulations that apply in your country. If in doubt, use a neutral wire of the same size as the live wire or wires.