answersLogoWhite

0

40000 / (400 x 1.732) = 57.7A

I'm assuming the 400v is a L-L voltage.

User Avatar

Wiki User

13y ago

What else can I help you with?

Related Questions

How many amps will a 240 volt single phase 15 kva generator supply?

62.5 amps


How many amps for 1010 KVA generator per phase?

To answer this question the voltage of the generator must be given.


How many amps does a 18000 watt generator supply at 240 volts?

75 Amps theoretically Need to know if the generator is 3 phase or single phase.


How many output amps is a 75 KVA generator single phase?

The formula you are looking for is , A = kva x 1000/Volts.


How many amps will a 240 volt single phase 20KW generator supply?

Typically 75 amps on natural gas, 85 amps using propane. Peak amps(for less than a second) to start a big appliance, like an A/C condenser, are 130.


How many output amps is a 75 KVA generator?

It depends upon the Generator system voltage. For 3 Phase, 600 Volt system, it will be 73 Amps For 3 Phase, 480 Volt system, it will be 90 Amps For 3 Phase, 208 Volt system, it will be 208 Amps


How many amperes for 3 phase 220v 5 tonner?

50 Amps Single Phase 20 Amps Three Phase


How many amps is 5.5KVA generator good for?

5.5kva


How many output amps is a 600kva generator at 240v?

To calculate the output amps of a 600kVA generator at 240V, you would use the formula Amps = kVA / Volts. In this case, it would be 600kVA / 240V = 2500 amps.


How many watt generator to run a 150 amp service?

You will need a 50 kW generator for a single phase 120/240 volt service.


How many amps 50 hp 240 3 phase?

106 amps


How many amps is 8500 watts generator?

To find the amperage of a generator, you can use the formula: Amps = Watts / Volts. Assuming a standard voltage of 120V for household generators, you can calculate the amperage as: 8500 Watts / 120 Volts = 70.83 Amps.