answersLogoWhite

0

250 kW= 250,000 watts

1 horsepower=746 watts (The motor is approx. 335 horsepower. (just FYI))

The Ohm's Law formula for this is:

P(Power in watts)=I(Current in amps) x E(Voltage)

Since the voltage is unknown, I will give you different options based on input voltage.

I will assume three phase power for a motor this size.

So, back to the formula:

250,000=I x E

Let's assume voltage (E) to be 480v:

250,000=I x 480

I=520 amps

For a voltage of 208 (much less likely for this size motor):

250,000=I x 208

I=1201 amps

These are 'running' currents only. The amount of starting current will be much, much higher, but only for a brief period.

Answer

The above answer assumes that the motor's input power is 250 kW. But this is not the case.

The power of a motor is always expressed in terms of its output power, not its input power! In North America, this is expressed in horse power, whereas everywhere else it's expressed in watts. So, to determine the current drawn by the motor, you have to start by determining its input power (input power is output power times efficiency); if you don't have a means of determining the motor's efficiency, then you cannot really find out its input power, in which case, you cannot find its current.

User Avatar

Wiki User

13y ago

Still curious? Ask our experts.

Chat with our AI personalities

DevinDevin
I've poured enough drinks to know that people don't always want advice—they just want to talk.
Chat with Devin
TaigaTaiga
Every great hero faces trials, and you—yes, YOU—are no exception!
Chat with Taiga
JordanJordan
Looking for a career mentor? I've seen my fair share of shake-ups.
Chat with Jordan
More answers

To answer your question, I need more info. What voltage are you using? IE. (12 volt, 24 volt, 120 volt, 240 volt) it makes a difference.

Use this formula ......... Watts = Amps x Volts

Amps = Watts / Volts

Volts = Watts / Amps

So figure out your voltage requirements, then use this formula to figure out

Amps Remember to give yourself a 20% margin.

Example 55 KW @ 120 Volts (55,000W / 120V = 458A)

458 - 20% = 366.4 Amps Available

Only use 80% of available Amps or Voltage otherwise your wiring

will heat-up over time and fail.

<<>>

To answer this question the voltage of the motor has to be known.

Comment

You also need to know its efficiency, because a motor is rated according to its output power*, not its input power. So, in this example, its input power will be less than 55 kW.

(*In North America a motor's output power is normally expressed in horsepower. Practically everywhere else, it's expressed in watts.)

User Avatar

Wiki User

13y ago
User Avatar

Add your answer:

Earn +20 pts
Q: How many amps will a 55 KW motor take?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

What is the armour cable size for 45kw 3phase ac motor 2965rpm?

At 2965 rpm it sounds like an induction motor for a 50 Hz supply. A 45 kW motor would draw about 55 kW from the supply with a power factor of 0.85, so that is 65 kVA, and on a 415 v 3-phase supply that is a current of 90 amps. For armoured XLPE cale the size needed is at least 16 mm2 Probably 25 mm2 would be preferred for a permanent installation but it would depend on how the cable is installed, how much free air movement there is around it etc.


What will be the size of cable for 75 HP 220 Volts 3 phase motor?

75 HP = 55 KW 55 = 31/2 x 0.220 x I x cos &phi; = 31/2 x 0.220 x 0.8 x I I = 55/(31/2 x 0.220 x 0.8) = 180,42 A 3 x 70 mm2 is the size of cable for 75 HP 220 Volts 3 phase motor


What is circuit breaker rating when electric load of a machine is 11.5 kW?

This question cannot be answered as asked. you would need to know also the voltage and phasing. Assuming we are dealing with 120-volt, single phase, 11,500 watts would be 55-running amps. Assuming we are dealing 208-volts, three phase, 11,500 watts would be 32 running amps and assuming we are dealing with 250-volt three phase, 11,500 watts would be 26.5 running amps. I hope I have answered your question.


What kind of outlet is needed for a sump pump?

Outlet rating should be suitable to the rating of the motor. The type should be preferably IP 55 or higher if mounted outside the sump in dry area.


What is the current carrying capacity of 10 awg wire?

For cables in 'Free Air', that is, not routed through conduit, it depends on the Temperature rating of the cable; 60 deg C: 40 amps, 75 deg C: 50 amps, 90 deg C: 55 amps As always, if you are in doubt about what to do, the best advice anyone should give you is to call a licensed electrician to advise what work is needed.Before you do any work yourself,on electrical circuits, equipment or appliances,always use a test meter to ensure the circuit is, in fact, de-energized.IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOBSAFELY AND COMPETENTLYREFER THIS WORK TO QUALIFIED PROFESSIONALS.