answersLogoWhite

0


Best Answer

1kw=1.25kva

by this relation 75kva=60kw

p=1.732*380*I*1

I=60000/1.732*380*1

I=91Amps

Comment

Power factor is irrelevant to this question. You don't need to convert the kV.A rating to kilowatts, simply divide 75 000 V.A by (1.732 x 380). The answer is 114 A.

This, of course, assumes that the question refers to a three-phase generator and that 380 V is the line voltage.

User Avatar

Wiki User

12y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

12y ago

On the 208v side: 208 amps

On the 480v side: 90 amps

Transformers are generally used from higher voltage to lower voltage but they can be used in either direction.

This answer is:
User Avatar

User Avatar

Wiki User

11y ago

Just divide 75,000 volt-amps by 240 and you will find the amps.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How many output amps is a 75 kva 208v-480v?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

How many output amps is a 75 KVA generator?

It depends upon the Generator system voltage. For 3 Phase, 600 Volt system, it will be 73 Amps For 3 Phase, 480 Volt system, it will be 90 Amps For 3 Phase, 208 Volt system, it will be 208 Amps


How do you calculate the output voltage of a transformer if kva rating is known?

You can't determine the output voltage of a transformer by knowing kva. Transformers will be marked as to input and output voltages. Some will have multiple input and output voltages. The output voltage depends on the ratio of coil turns between input and output.


How many output amps is a 75 kva transformer?

For single phase, KVA = (line to ground) * (phase current). A 75kVA 480 to 208Y/120 volt transformer is a fairly common transformer. I assume this is the type of transformer you are referring to. 75k / 120 = 625 Amps. As an FYI, the 208Y voltage is the line to line voltage, which is equal to (phase 1) - (phase 2), where the phases are separated by 120 degrees, thus (phase 1) * 1.732 For three phase, kVA = (line to line voltage) * (phase current) *(sqrt 3), 75k / 208 / 1.732 = 208 Amps.


How do you convert Amps to KVA for a single phase system?

use 1.0 as your PF Understand that K=1000, so KVA simply means thousands of volts times amps. First, multiply KVA by 1000 to get VA, then divide by the voltage of the system to get amps. Example: 6KVA, 240V single-phase. 6 * 1000 = 6000 VA 6000 / 240 = 25A


How many amps are in 15000 KVA 480 3 phase?

The formula to find amps is: I = (KVA x 1000)/(E x 1.73) I = (2500 x 1000) / (480 x 1.73) I = 2500000 / 830.4 I = 3010.597A

Related questions

How many output amps is a 75 KVA generator single phase?

The formula you are looking for is , A = kva x 1000/Volts.


How many amps can you get from a 500Kva transformer?

The amps you can get from a 500 kVA transformer would depend on the voltage of the transformer's output. To calculate amperage, you can use the formula: Amps = Power (kVA) / Voltage. For example, if the output voltage is 480V, you would get approximately 1041 amps (500 kVA / 480V).


How many output amps is a 600kva generator at 240v?

To calculate the output amps of a 600kVA generator at 240V, you would use the formula Amps = kVA / Volts. In this case, it would be 600kVA / 240V = 2500 amps.


How many output amps is a 75 KVA generator?

It depends upon the Generator system voltage. For 3 Phase, 600 Volt system, it will be 73 Amps For 3 Phase, 480 Volt system, it will be 90 Amps For 3 Phase, 208 Volt system, it will be 208 Amps


Can you use a step up transformer 110220 with output of 16 kva?

Yes, but your input current is going to be high at 133 amps. The output of the transformer is not going to be 16 KVA, that is the rating of the transformer.


How many KVA is 62 amps?

At what voltage? When you know the voltage then, to get the amps those kilovolt-amps contain, you simply divide the kilovolt-amps by the voltage.


How many output amps is a 45 kva transformer?

There is not enough information provided to answer. KVA is short for "Kilo Volt Amperes". That is, thousands of Volt Amps. In order to determine how many Amperes are flowing, you must know at what voltage it is operating. Amperes = 45,000 ÷ volts Bill Slugg


How many output amps from a 75kva transformer fed with 480 ckt.?

It depends on what the output voltage is. You only specified the input voltage, not the output voltage. The equation is 75 Kva = {some} amps times {some} kilovolts. (Minus incidental losses, of course, but you still need to know output volts.)


How many kva on 88.88 amps in 1phase secondary 230 volts?

20.44 kva


How do you calculate the output voltage of a transformer if kva rating is known?

You can't determine the output voltage of a transformer by knowing kva. Transformers will be marked as to input and output voltages. Some will have multiple input and output voltages. The output voltage depends on the ratio of coil turns between input and output.


500kva how many amps given capacity?

500 KVA how many amps? almost 650 Amps according to formula.


How many amps will a 240 volt single phase 15 kva generator supply?

62.5 amps