The quick way is to find a cable size table and look it up. The calculation is complicated so most people use tables of pre-calculated values.
It complicated because the current you can run through a cable depends on the cooling of the cable. Current passing through a cable with greater than zero resistance, which is normal, will generate heat in proportion to the square of the current and the resistance of the wire.
If you can keep the cable cool enough to stop it melting then it will carry that current. But cooling a cable depends on a lot of factors, especially the insulation on the cable. Electrical insulation, to keep the electricity inside the cable, also keeps heat inside the cable, so most power distribution cables run quite warm to the touch. They are limited by the softening and melting point of the plastic insulation that is commonly used.
Even overhead cables, insulated and cooled by air, run warm, but its not recommended to try and touch them.
445 amps. For example Mulberry AAAC cable.
25 amps
the current rating of a 70mm swa 3core cable is 1.2 amps buried or 2 amps on perforated cable tray suspended 500 feet above sea level in antartica
Not enough information. To answer this question the amount of current in AMPS the circuit is drawing is needed.
25 amps, 6000 watts
To determine the cable size in mm2 required for 450 amps, you need to consider the current-carrying capacity of the cable. The exact size will depend on the type of cable and the installation conditions. For 450 amps, heavy-duty cables with a size of around 240 mm2 or larger would typically be used to ensure safe and efficient operation.
A parallel run of 750 MCM AWG conductors will handle 1000 amps. if we want 1000amps to flow, 250sqmm cable is enough.
It is a HUGE amount of current 1000 amps
what is current capacity of 95 sqmm cable?
Amps is a measurement of current. Watts (or kilowatts) is a measure of power. To get the power from the current, you have to know the electrical potential or volts used to produce the current. Amps × Volts = Watts (or Current × Electrical Potential = Power). Incidentally, a kilowatt is 1000 watts, so you'll have to divide your answer by 1000. e.g. if your volts is 40, then 25 amps × 40 volts = 1000 watts. 1000 watts (divided by 1000) is 1kw or kilowatt.
445 amps. For example Mulberry AAAC cable.
25 amps
64 AMPS
30 Amps
Current or AMPS are what the appliance draws or load of the appliance. So, if you have a say 10,000 amps going thru a cable rated for say 1,000 amps , guess what ,the cable over heats and either will melt or at least catch fire.
Volts and amps measure two different things. Volts are used to measure potential difference. Amperes (amps for short) are used to measure current. Compare it to a garden hosepipe: Voltage corresponds to the pressure of the water, current measures how fast the water flows. 2000 millivolts equals two volts. For comparison, a single AA cell gives 1.5 volts. 1000 amps is several times the current used by the average household. A regular AA cell can provide, at maximum, about half an amp.
2.5 sqmm cu cable current carrying capacity is 19 amps.