answersLogoWhite

0


Best Answer

A ground fault circuit interrupter is as its name implies, a device (circuit breaker or special receptacle) which interrupts (shuts down) a circuit when it detects a ground fault (current flowing to ground). When a small amount of current (4 to 6 milliamperes) is detected flowing to ground by the electronics within the device it trips so that no more current can flow, thereby possibly saving your life. Example: you are listening to the radio while having a bath and it falls into the tub--- the circuit will turn off before you can be harmed. GFCI's as they are commonly called are required by the Electrical Code to be installed in bathrooms, kitchens where the receptacle is within one meter of the sink, any outdoor location (rain and snow) and any other wet or damp locations. (refer to code book) An Arc Fault Circuit Interrupter is a device( I've seem breakers but am unsure whether there is a special AFCI receptacle) which shuts off a circuit when it detects an arcing condition in the circuit. An example of arcing would be when you pull the plug out of a wall receptacle when the device plugged in is under load (turned on) and you see a little (sometimes big depending on the size of the load) bluish or yellowish flash or "arc". Receptacles on AFCI circuit breakers are required by the electrical code to be installed in bedrooms. It has something to do with the flammability of linens and blankets I believe, but here again for detailed info please consult the official Electrical Code book for your location.

User Avatar

Wiki User

13y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

14y ago

A ground fault breaker, or outlet can tell when the current leaks to a different ground.

These are used when or in the area of water.

An ARC fault breaker can tell when an Arc occurs, such as the hot line contacting the neutral, which causes an ARC and has lead to sparks and fires. Most new construction homes have ARC fault breakers for bedrooms.

This answer is:
User Avatar

User Avatar

Wiki User

9y ago

Simplified, an arc can occur without tripping a breaker. An arc is often the result of a poor connection or a worn contact on a switch. Equipment plugged in to an outlet will draw current. While drawing current, an attachment screw on the outlet may be loose. This is high resistance. Volts equal amps x resistance. While the equipment is drawing current, the poor contact surface at the screw will slightly arc, often barely perceptible but extreme local heat is generated. The small, high temperature arc can cause a fire over time. These are sneaky little trouble makers. The AFCI breaker detects the noise associated with arcing and will trip.

GFCI breakers simply compare line current to load current. When 5mA or more is unaccounted for, the breaker trips.

Arc fault breakers were first required for bedrooms because so many fires were created by bedroom extension cords and lamp cords that shorted and arced. A GFCI would not detect that fault.

This answer is:
User Avatar

User Avatar

Wiki User

12y ago

They are totally different. The GFCI is used to protect you from an electrical shock but an AFCI is used to prevent a fire. A GFCI will detect any measurable difference in the voltage returning to the circuit and shut the circuit off when it is detected. A AFCI breaker will detect a spark or arc which causes overheating of the outlet or wiring. It will turn the circuit off when it detects a spark or arc.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What is the difference between an arc fault breaker and and a ground fault breaker?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Engineering

Do you need a ground fault breaker for your hot tub?

Yes, the electrical code requires a ground fault breaker for your hot tub.


What is difference between shunt trip and ground fault circuit breaker?

Ground fault breakers monitor the current on the neutral wire flowing back to the neutral bar, a 4 to 6mA difference will trip the breaker, Shunt trip breakers on the other hand can be tripped remotely from some other type of switch or location. In industrial applications it is used to shut power off in an emergency situation, when access to an electrical panel may denied.


What is a Class A circuit breaker?

A Class "A" Circuit breaker is a Ground Fault Interrupt (GFI or GFCI) breaker ."Class A" marking -- A "Class A" ground-fault device is intended to protect people. The Class A marking indicates that the trip threshold of the GFCI is between 4 mA and 6 mA. This marking may be in any location except the back.


Will a faulty ground fault circuit interrupt device cause spurious breaker trips?

yes


Why is a ground fault circuit interrupter necessary for electrical devices that are used around water?

Water could provide a path to ground for current. This path may be fairly high impedance; high enough that a standard breaker protecting the device would not operate. A ground fault interruptor is used to sense a "loss of current" to ground between the source and its' return. this can be much more sensitive compared to a typical overload breaker, and so provides better protection for this type of situation.

Related questions

Do you need a ground fault breaker for your hot tub?

Yes, the electrical code requires a ground fault breaker for your hot tub.


What do ground fault relays do?

Ground fault relays sense ground faults in the circuit and trigger a circuit breaker to trip off


What is a difference between ground fault and earth fault?

An earth fault relay and an overcurrent relay are both protective devices used in electrical systems, but they serve different purposes and operate based on different principles. Here are the key differences:Function:Earth Fault Relay: Detects ground (earth) faults, which occur when a live conductor comes into contact with the earth or a grounded component. Its primary function is to sense leakage currents to the ground and trip the circuit breaker to prevent damage or hazards.Overcurrent Relay: Detects overcurrent conditions, which occur when the current exceeds the rated capacity of the circuit. This could be due to overloads or short circuits. Its primary function is to protect the electrical system from excessive current that can cause overheating and damage.Detection Method:Earth Fault Relay: Typically uses a zero-sequence current transformer (CT) or residual connection method to measure the imbalance between phase currents, which indicates a ground fault.Overcurrent Relay: Uses current transformers (CTs) to measure the current in each phase and operates when the current exceeds a predetermined threshold.Sensitivity:Earth Fault Relay: More sensitive to small currents, as earth faults often involve low fault currents compared to phase-to-phase faults.Overcurrent Relay: Designed to detect larger currents that exceed the normal operating range of the circuit.Applications:Earth Fault Relay: Commonly used in systems where protection against ground faults is critical, such as in power distribution networks, industrial installations, and consumer units.Overcurrent Relay: Widely used in protecting transformers, motors, generators, and feeders from overcurrent conditions.Configuration:Earth Fault Relay: Usually configured to operate at a lower current setting due to the nature of ground faults.Overcurrent Relay: Configured based on the normal operating current of the circuit and its protection requirements, usually at a higher current setting than earth fault relays.In summary, while both relays are crucial for system protection, an earth fault relay focuses on detecting and isolating ground faults, whereas an overcurrent relay protects against excessive current conditions that can damage equipment and cause safety hazards.


What is the difference between a fault and a fold?

a fault is a large crack in the earth. a fold is when the ground gets bent.


What is difference between shunt trip and ground fault circuit breaker?

Ground fault breakers monitor the current on the neutral wire flowing back to the neutral bar, a 4 to 6mA difference will trip the breaker, Shunt trip breakers on the other hand can be tripped remotely from some other type of switch or location. In industrial applications it is used to shut power off in an emergency situation, when access to an electrical panel may denied.


A GFCI device in a breaker is intended to?

A GFCI device in a breaker is intended to trip the breaker open when a ground fault is sensed in the circuit that the breaker is protecting.


What is a Class A circuit breaker?

A Class "A" Circuit breaker is a Ground Fault Interrupt (GFI or GFCI) breaker ."Class A" marking -- A "Class A" ground-fault device is intended to protect people. The Class A marking indicates that the trip threshold of the GFCI is between 4 mA and 6 mA. This marking may be in any location except the back.


What causes the main breaker to trip from a fault current from a twenty amp branch circuit?

A fault current on a twenty amp branch circuit can cause the main breaker to trip due to the higher-than-normal flow of electricity, which exceeds the circuit's capacity. This could be caused by a short circuit (abnormal connection between conductors) or a ground fault (unintended connection between a conductor and ground). The main breaker detects this overload and trips to prevent overheating and potential fire hazards.


If live is kept open could it trip circuit breaker by connecting neutral to ground?

Yes, keeping a live wire open can potentially trip a circuit breaker if the neutral and ground are connected. This can create a potential difference between neutral and ground, leading to a fault current that may trip the breaker. It is unsafe to have a live wire left open and in contact with other conductors.


How a 240 V GFCI breaker works without a neutral ran to the equipment?

A 240V GFCI breaker monitors the difference in current between the hot wires, providing ground-fault protection without needing a neutral wire. It compares the current on both hot wires and trips if an imbalance is detected, indicating a ground fault. This system does not rely on a neutral wire to detect faults and protect against electrical shocks.


How do you express an earth leakage circuit breaker?

In North America they are known as a GFCI. Ground Fault Circuit Interrupter breaker.


How do you wire a ground fault switch?

To replace the wire ground fault switch, you need to switch off electric power from the source. After switching it off you can use the screwdriver to open screw and remove the faulty switch and replace it with a good one. <<>> There is no such a device as a ground fault switch. There is a ground fault breaker and a ground fault receptacle.