answersLogoWhite

0


Best Answer

An earth leakage relay is an electronic or electromechanical device that detects the current flowing to earth (Americans call this ground). If this earth leakage current is above a preset level (and carries on for a preset time) the relay is "tripped" - this may switch on an alarm signal - or more usually it simply disconnects the supply. Currents may flow to earth due to a fault condition or because of lots of individual items connected to the supply have a small "leakage" to earth.

User Avatar

Wiki User

βˆ™ 14y ago
This answer is:
User Avatar
More answers
User Avatar

Wiki User

βˆ™ 10y ago

On a supply that is working normally the current in the live and neutral are exactly balanced, with no current in the earth.

In fault conditions the live may become connected to the earth inside the faulty equipment, or in some other way, which causes some current to flow in the earth wire. In the worst case this could be caused by someone suffering an electric shock. The ELCB detects this and causes the supply to be disconnected.

ELCBs are usually set to trip on small currents, 10-30 mA,

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 12y ago

An earth-leakage relay is a protective device used to detect any leakage current flowing to earth, and to initiate the disconnection of the affected circuit. The relay is supplied by means of a current transformer through which the earth conductor passes.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 11y ago

An earth leakage circuit breaker actually protects the ground (earth ground) of , usually, sensitive electronic equipment that could be damaged is there is the slightest current found on the ground. Usually if that type of fuse or breaker is tripped or blown, the equipment will not turn on. This type of equipment is mostly used in the Medical Field.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 6y ago

If the live wire (phase) touches the body of the equipment, then there is current flow in the earth wire, which is sensed by the ELCB which cuts off the circuit to avoid shock to the personnel.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 12y ago

It is a physical electric circuit, that protects humans against electrical shocks. it has two types, voltage based and current based.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 12y ago

used to detect any fault in electrical circuit.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 14y ago

Earth leakage relay trips when the neutral to ground voltage limit exceeds certain limit and there is a current flow from neutral to ground

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What is the operation of earth leakage relay?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

Can loose neutral wire effect the operation of Earth Leakage Circuit Breaker?

Yes, a loose neutral wire can effect the operation of Earth Leakage Circuit Breaker.


Circuit diagram of stand by earth fault relay?

earth fault relay is similar like earth leakage ralay,but the 2nd one is more sensitiv.


What is the difference between Earth Fault Relay and Earth Leakage Relay?

Earth leakage relays are instantaneous tripping relays where as earth fault relays have the option of time and ampere setting i.e. for a setted ampere the circuit breaker will be tripped off after the setted time (in second).


What is a restricted earth neutral system?

A restricted earth-neutral system is a type of electrical system where the neutral conductor is not directly connected to earth ground. Instead, it is connected through a specific impedance. This system is designed to limit the current flow in case of a ground fault to provide a safer operation in certain environments.


What are two electrical devices for South Africa is regarded as a world leader?

earth leakage relay and miniature circuit breakers (MCB)


Draw and explain the operation of fault voltage ELCB and residual current device?

ELCB means Earth Leakage Circuit Breaker -- it is used to trip the Circuit breaker if any leakage fault occured means


Earth fault relay and an overcurrent relay Methods to energise an earth fault relay?

Earth fault relay and an over current relay Methods to energies an earth fault relay with simulation diagram?


How do you solve earth leakage?

The best way to stop earth leakage is to make sure that the are no active circuits going to ground. This will help keep the circuit running right.


What is ELDB in electrical?

ELDB is Earth Leakage distribution board it is used for earth fault.


Will the earth leakage relay protect me if i hold the bare neutral wire and then touch the bare live wire?

It definitely will NOT protect you because the ELR will not trip for a current going up the live and coming back down the neutral.


How does an earth leakage transformer work?

What is the definition of earthing and how it works?


What is an earth fault relay?

An earth fault relay is a relay that is activated by a fault current that flows from the power line to the earth. Earth fault relays are found in power distribution systems.