First of all you need to observe maximum current at various possible supply condition (i. e. 220VAC to 260VAC). Then check the inrush current for the equipment. When you start an high power device then it draws 4 times more current than usual. Your fuse should also take care of inrush current.

For example: if maximum possible current is 500mA then your inrush current may go upto 2A. Thus if you put a fuse of 600mA then everytime you turn on the device, it may burn the fuse. So the suitable fuse for such condition is 2A

User Avatar

Wiki User

14y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How do you calculate fuse rating?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What is the correct formula to calculate a fuse rating?

watts Divided by Volts = amps


How do you calculate the fuse rating level if the full load is 4 amp?

To calculate the fuse rating level, you typically want to choose a fuse that is slightly higher than the full-load current to avoid nuisance tripping. For a full load of 4 amps, you could choose a fuse rating of 5 or 6 amps.


A transformer is rated at 12V-0-12V and 250mA so what does the 250mA mean and how do you calculate the fuse for the primary winding without knowing the VA rating?

A: The VA rating is there 6v/a the power fuse to blow is 6watts. 050a fuse


It is ok to use a fuse with a higher amperage rating and not ok to use a fuse with a smaller amperage rating why?

It is ok to use a fuse with a higher amperage rating and not ok to use a fuse with a smaller amperage rating why?


What is the fuse rating of 600watt appliance on a 220 volt supply?

To calculate the fuse rating for a 600 watt appliance on a 220 volt supply, you can use the formula: Fuse rating = (Power/Voltage). In this case, it would be 600 watts / 220 volts, which equals approximately 2.73 amps. Therefore, you would need a 3 amp fuse for the 600 watt appliance on a 220 volt supply.


What happens if you use a fuse that's overrated for voltage but has the correct current rating?

Using a fuse correctly rated for current but "overrated" for voltage does not present a problem. Current ratings are critical safety issues, and fuses should be replaced with those of the same current rating. But using a fuse with an identical current rating but a higher voltage rating is not a problem. The reason for that lies in what the voltage rating of a fuse is. Fuses are given a voltage rating to state a maximum voltage in a circuit that they are designed to protect. And the voltage rating has nothing to do with the "normal" operation of the fuse. The fuse carries current when it operates normally, but when something happens and excessive current flows, the fusible link heats up and opens. This is where the voltage rating comes into play. It is possible that a fuse can arc through when it fails. It is the voltage rating that stands in the way of this. As long as the voltage rating of a circuit is not beyond the voltage rating of the fuse, that fuse will fail safely when it fails. It is acceptable to use a fuse of an equal current rating but a higher voltage rating when replacing a fuse that has failed.


What is the current rating of T2L 250v fuse?

The current rating is 2A (2 amps).


What minimum fuse rating is needed for a 12volt curcuit with a 36 watt bulb?

To calculate the minimum fuse rating needed for a 36W bulb on a 12V circuit, divide the wattage by the voltage (36W / 12V = 3A). Therefore, a minimum 3A fuse would be sufficient for a 36W bulb on a 12V circuit.


What is meant by ratting of fuse?

A fuse is given a various rating (strength). For instance, a home appliance (washing machine, etc) would usually have a fuse with a 13 amp rating. While a low powered lamp would only merit a 2 or 5 amp fuse rating. It is important to use a fuse of the correct rating in amps for each electrical appliance.


How is the minimum fusing current related to the current rating of a fuse?

Each fuse has its own rating. It will be marked on the fuse somewhere.


What is the maximum current that can flow through a fuse?

A current rating of a fuse is designed to open a circuit at a specific current flow. This rating is imprinted on the fuse and lets you know what the maximum amount of current the fuse is designed to open at. A fuse is in the circuit to protect the conductor that the current flows through. Never over fuse a conductor's current carrying capacity.


What is the fuse rating for a kettle?

A standard 3kW immersion heater will require a fuse rating of 13 A. This is because, it draws a current of 12 A.