answersLogoWhite

0

I'm sure you could, but it wouldn't be practical. The reason for this is because 208 volts between two phases comes from a three phase transformer, while 240 volts phase to phase comes from a single phase, center tapped transformer. If you're asking regarding a resistive load, such as a heater, the load should work with 240 volts or 208 volts. There will be a slight difference in performance, but it shouldn't be very noticeable. If you're asking because you have a motor load rated for 208v, you'll likely see that the motor requires three phase 208 volt power and you only have 'two phase' 240v power. You can however supply a three phase equipment or motor with a device called a phase converter.

User Avatar

Wiki User

16y ago

What else can I help you with?

Continue Learning about Movies & Television
Related Questions

What happens when 240 volt equipment is plugged into a 208 volt source?

It should be ok


Can you convert 110 volt to 240 volt?

Yes


Normal voltage house in the US?

The vast majority of homes are supplied with 120/240 volt or 110/208 volt.


Do you need a step down transformer to run a 208 volt steam table on 240 volt feed?

Yes a transformer should be used. The steam table needs its correct voltage otherwise on 240 volts it will operate over its given specified nameplate wattage. A 208 volt heating element run off of 240 volt will have an output increase by 75 percent.


How can I convert a 240 volt power source to a 120 volt power source using a 240 volt to 120 volt adapter?

To convert a 240 volt power source to a 120 volt power source using a 240 volt to 120 volt adapter, simply plug the adapter into the 240 volt outlet and then plug your 120 volt device into the adapter. The adapter will step down the voltage from 240 volts to 120 volts, allowing you to safely power your device. Make sure the adapter is rated for the appropriate wattage to avoid damaging your device.


Do all electric ovens cooktops ranges and clothes dryers operate on 208v as well as 240v?

No, use only the voltage for the appliance that your utility system is supplying to your residence. If your system is 208 volts use 208 volt appliances. Likewise if the utility system is 240 volts use only 240 volt appliances. 208 appliances on 240 will overheat the appliances and 240 appliances on 208 will not produce the wattages that the manufacturer recommends for cooking and drying.


Can you run a 208 volt single-phase computer off 240 volt power?

No. The 1-phase 240 setting on your computer's power supply is for the 240V wall outlets in other countries. The 240 outlets in your home are 2-phase 240.


What is a 208 circuit?

The 208 volt configuration is one phase of a three phase source at 240 volts, where the 208 volt circuit is connected between the center tap of one 240 volt phase (usually a grounded neutral, in the style of a standard 120/240 split phase system) and the high delta connection on either of the other two phases. 208 circuit would consist of two phases of a 208 volt wye system or could be all three phases. The voltage between conductors would be 208 volts. The voltage to ground from any phase would be 120 volts. A 240 volt delta system would give you a high leg to ground, somewhere around 190 volts and the other two would be 120 volts to ground.


How do you convert 208 volt amps to 480 volt amps?

Add another leg of 120 to a three pole breaker.


What is the maximum volts that can be used on a 208 230 volt motor?

You should not go above 240 volts for that type of motor.


You have 240v and you need to convert to 230v for an air compressor?

Yes, you can use a 230 volt device on a 240 volt supply.


Does a 208 volt outlet need a neutral?

No a 208 volt outlet does not need a neutral. 208 volts is the line voltage between any two legs of a three phase 208 volt system.