answersLogoWhite

0

If you have 100 amp wire, you can use it for a 60 amp circuit, or for any circuit of 100 amps or less.

But if you have a 60 amp circuit, 60 amp wire is thinner and cheaper than 100 amp wire.

User Avatar

Wiki User

13y ago

What else can I help you with?

Continue Learning about Natural Sciences

What size wire and circuit breaker is needed for an electric oven 4 wires with rated load of 34.9 amps 220v that is about 100 foot run from the electrical panel?

That would be a 40 amp 220v circuit. Circuit breaker is 40 amps and wire is 8 awg. Should use solid copper wire. Follow oven installation instructions.


What happen when a fuse wire of 100 ampere is used when a circuit at home draws a maximum current of 20 ampere?

If a 100 ampere fuse wire is used in a circuit where the maximum current drawn is 20 ampere, the fuse wire will not blow as the current is below the rated capacity of the fuse. The fuse wire is designed to protect the circuit by blowing and breaking the circuit when the current exceeds its rated capacity, preventing damage to the circuit components.


What wire 240 volts 6500 watts 100 ft?

The sizing of wire is calculated by the amount of current the circuit draws. To find the amperage when the wattage is known use the following formula, Amps = Watts/Volts. 6500/240 = 27 amps. A #10 AWG copper conductor will limit the voltage drop to 3% or less, when supplying 27 amps at 240 volts for a 100 foot distance.


What gauge cable to run 240 volts?

For a 240-volt circuit, you should use a cable with a gauge appropriate for the amperage of the circuit. Commonly used sizes include 10-gauge wire for up to 30 amps, 8-gauge wire for up to 40 amps, and 6-gauge wire for up to 55 amps. Ensure to consult local building codes and a qualified electrician for specific requirements.


What size of wire is required for 20 amps 220v over 100 ft?

For a 20 amp, 220V circuit over a 100 ft distance, you would ideally use a 10 gauge wire to minimize voltage drop and ensure safety. A 10 gauge wire can safely handle 20 amps of current and is appropriate for this application.

Related Questions

What size wire and circuit breaker is needed for an electric oven 4 wires with rated load of 34.9 amps 220v that is about 100 foot run from the electrical panel?

That would be a 40 amp 220v circuit. Circuit breaker is 40 amps and wire is 8 awg. Should use solid copper wire. Follow oven installation instructions.


What happen when a fuse wire of 100 ampere is used when a circuit at home draws a maximum current of 20 ampere?

If a 100 ampere fuse wire is used in a circuit where the maximum current drawn is 20 ampere, the fuse wire will not blow as the current is below the rated capacity of the fuse. The fuse wire is designed to protect the circuit by blowing and breaking the circuit when the current exceeds its rated capacity, preventing damage to the circuit components.


What is the maximum current capacity of a 100 amp circuit breaker?

The maximum current capacity of a 100 amp circuit breaker is 100 amps.


What wire size is good for 100 amps?

# 4 copper wire short distance.


How many amps is 3 awg wire good for?

It depends on the application, but for Single-Phase dwelling service and feeders 3 AWG copper is good for 110 amps. That really equates to 100 amps since you can't get a 110 amp circuit breaker.


What is the appropriate wire gauge for a 100 amp electrical circuit?

The appropriate wire gauge for a 100 amp electrical circuit is typically 3 AWG copper wire.


What wire 240 volts 6500 watts 100 ft?

The sizing of wire is calculated by the amount of current the circuit draws. To find the amperage when the wattage is known use the following formula, Amps = Watts/Volts. 6500/240 = 27 amps. A #10 AWG copper conductor will limit the voltage drop to 3% or less, when supplying 27 amps at 240 volts for a 100 foot distance.


What is the recommended wire size for a 100 amp circuit using THHN wire?

The recommended wire size for a 100 amp circuit using THHN wire is typically 3 AWG (American Wire Gauge).


What gauge cable to run 240 volts?

For a 240-volt circuit, you should use a cable with a gauge appropriate for the amperage of the circuit. Commonly used sizes include 10-gauge wire for up to 30 amps, 8-gauge wire for up to 40 amps, and 6-gauge wire for up to 55 amps. Ensure to consult local building codes and a qualified electrician for specific requirements.


What is the recommended gauge of wire for a 100 amp electrical circuit?

The recommended gauge of wire for a 100 amp electrical circuit is typically 4 AWG (American Wire Gauge).


What size of wire is required for 20 amps 220v over 100 ft?

For a 20 amp, 220V circuit over a 100 ft distance, you would ideally use a 10 gauge wire to minimize voltage drop and ensure safety. A 10 gauge wire can safely handle 20 amps of current and is appropriate for this application.


What wire size to carry 16 amps 100 ft?

14