well, the easy answer is, black wire to one pole of the breaker, white wire to the neutral bus with all the other white wires, bare wire to the ground bus with all the other bare (or green) wires. BUT the breaker must be 20 amps or less for residential outlets and you much match the wire size to the breaker, #14 for 15 amp breaker, #12 for a 20 amp breaker AND if there is only going to be one outlet, if it is a 20 amp circuit, the outlet has to be rated for 20 amps. Yes, but why would you want to? It is unclear to anybody else what you are doing and therefore a hazard. Do it right. Use a single pole breaker designed for 110V.
See Discussion Page
A breaker trips when there is too much current. If you unplug everything on the circuit and the breaker still trips then you have a wiring problem or a bad breaker. From your description it is not possible to be certain if the problem started when you installed new outlet or previously. You have to describe your problem in better detail to get a good answer. When you have a circuit that trips the corresponding breaker, you need to go through each outlet on the circuit and rule it out as the problem. This can be done by pulling each outlet, from the wall and systematically remove wires from outlets while power is off and determining when problem goes away.
If the GFI outlet is tripped (the outlet, not the breaker) then it is telling you there is a ground fault which must be fixed. If the GFI outlet is not tripped, and the breaker is not tripped, but it is still not providing power, then you have a loose connection or a wiring error.
First, check the circuit breakers; make sure they are all ON. Find out if any other outlets on the same breaker are working; it's always possible that a breaker is faulty. If the breaker is on and everything else on the circuit is working, it could be as simple as a poor connection inside the outlet. Also even though the outlet is not a GFCI, it may be fed from a GFCI outlet. Check near by outlets to see if any are GFCI and are tripped.
Yes, you can always have heavier wire than code requires.
If you can plug the fridge into another outlet and it comes on, then the issue is either a bad outlet connection or the circut breaker may be going out and needs replacement. Try the fridge on another outlet 1st. If it trips that one too then there is a short in your fridge.
Not if the GFCI breaker is supplying the circuit you are wanting to put the GFCI receptacle into.
A breaker trips when there is too much current. If you unplug everything on the circuit and the breaker still trips then you have a wiring problem or a bad breaker. From your description it is not possible to be certain if the problem started when you installed new outlet or previously. You have to describe your problem in better detail to get a good answer. When you have a circuit that trips the corresponding breaker, you need to go through each outlet on the circuit and rule it out as the problem. This can be done by pulling each outlet, from the wall and systematically remove wires from outlets while power is off and determining when problem goes away.
Circuit breakers can degrade over time but it would be better to get a competant electrician to do it. It might also mean you have too many things plugged into one outlet. Sometimes one circuit breaker may protect several outlets so it might be tripping because of a change in another outlet. ELECTRICTY IS DANGEROUS!!!! Don't do it yourself.
If the GFI outlet is tripped (the outlet, not the breaker) then it is telling you there is a ground fault which must be fixed. If the GFI outlet is not tripped, and the breaker is not tripped, but it is still not providing power, then you have a loose connection or a wiring error.
First, check the circuit breakers; make sure they are all ON. Find out if any other outlets on the same breaker are working; it's always possible that a breaker is faulty. If the breaker is on and everything else on the circuit is working, it could be as simple as a poor connection inside the outlet. Also even though the outlet is not a GFCI, it may be fed from a GFCI outlet. Check near by outlets to see if any are GFCI and are tripped.
Go to your distribution panel and shut off the breaker that you think is the circuit in question. If the circuit becomes de-energized then the breaker you just turned off feeds that circuit. Look on the handle of the breaker and the number you see is the amperage of that circuit. <<>> Determination of a 15 or 20 Ampere circuit is normally indicated by a combination of a 20A breaker and a 20A dedicated outlet. A 15A circuit normally has multiple outlets; not typical in a 20A circuit.
It means the breaker has been tripped. There are two possible ways to reset it - some have a button on the outlet (there may be several outlets on one circuit, so you may have to look around) the other is the main breaker in your breaker box. You'll need to find a reset the breaker.
the circuit breaker used will be miniature circuit breaker(MCB) maily used in homes.Answer for USA, Canada and countries running a 60 Hertz supply service.A two pole circuit breaker is used for a load of 240 volts. It is sized, according to the load amps of the device, to protect the wires that supply the load current.
Yes, you can always have heavier wire than code requires.
The size breaker you use is determined by the size wire used in the circuit. If you use AWG #12/2 wire then use a 20 amp breaker. If you use AWG # 14/2 then use a 15 amp breaker.
Deoends on code you are governed by. In USA, a GFCI outlet or a circuit controlled by a GFCI circuit breaker would be required.
If you can plug the fridge into another outlet and it comes on, then the issue is either a bad outlet connection or the circut breaker may be going out and needs replacement. Try the fridge on another outlet 1st. If it trips that one too then there is a short in your fridge.