The device could be faulty or it could be working perfectly, as they typically do. If you mess about with it without understanding how it works you could receive a life threatening shock. Another likely possibility, as GFCIs are extremely sensitive, is that you have plugged in a piece of equipment which is faulty and that equipment should therefore be thrown away.
<><><>
Depending on what is happening, there could be several possibilities:
A) You have put too many items onto the circuit the GFCI is protecting, so it cannot sense properly and trips, or
B) You have not had it installed correctly, and the Sense Ground wire has become corroded with time and moisture, or
C) The wiring that is further down the line, if it "protects" other sockets and circuits downstream from this one, have problems with the insulation breaking down, or
D) Something else is wrong and you need to call a competent person to advise on your home wiring.
<><><>
If the gfci trips this means there is more than 10mA current between the ground the hot and neutral wires which, in, say, a kitchen or outside the home or in some other damp area, usually means something got wet.
2. If the particular circuit's main circuit breaker has tripped then this particular GFCI outlet cannot be reset and it won't test either, with the power out. If you can reset the circuit's main circuit breaker at the panel, you may then find the GFCI works. A second outlet somewhere in the same room or elsewhere might also not have worked because it is connected to the load terminals of the tripped GFCI.
3. If the circuit's main circuit breaker at the panel can be reset and the GFCI still won't work then you may have a damaged GFCI or there may be some equipment still plugged into it - or into a second outlet somewhere in the same room or elsewhere - that has a fault. so if there is no equipment plugged in anywhere, either at or after the GFCI, get the GFCI replaced.
4. I suggest you probably should call an electrician.
<><><>
The Capacitor on a single phase motor (for a "fan", etc.) sometimes causes a GFCI to trip. Commercial Grade GFCIs are better suited to this application.
<><><>
Two other things can cause false tripping:
1. A noise filter or surge protector in the circuit after the GFCI bypasses high frequency noise to ground. This unbalances the current in the hot and neutral, tripping the device.
2. Dirt or insects inside the outlet box. One time I opened an outlet box that was tripping the GFCI even with no plug in the socket. The box was full of dead roaches. I removed the bugs, and the device started working normally.
<><><>
GFCI circuit breakers perform two functions. If it is a true circuit breaker it will prevent "over-current" conditions from overheating the wiring of your home and hopefully minimize the potential for fire. All circuit breakers and fuses are designed to 'trip' or 'blow' when an over-current condition exists. GFCI circuits have an additional function. To prevent or minimize the potential for hazardous shocks, GFCI circuits compare the current that goes across the two wires that make up the hot and common voltage lines of an outlet. If the current on the two wires does not match precisely, the assumption is that current is being lost to something outside of the circuit. This condition is called a "ground fault". In simple terms, it means that there is high potential that YOU are grounded, as in standing in a puddle of water, and YOU have touched the "hot" side of the circuit or the device somehow allows current to go outside of the normal voltage path. A ground fault can exist if an outside outlet has become wet with rainwater, or an outside extension cord is laying in water or an appliance is in the process of failing and voltage leaks to the ground wire. But as already mentioned, it can also indicate that the GFCI has failed, although that doesn't often happen.
<><><>
A GFCI [Ground Fault Circuit Interrupter] trips when it senses a ground fault. In a correctly wired circuit the return path should be on the neutral wire. The circuit will trip if the GFCI senses a difference in the current (amps) in the Black "hot wire" from what is returning in the White "neutral wire". The two current values should be the same unless you are leaking electricity, which is called a ground fault. This can happen in a wet location when electricity is using the water as its ground and not returning back through the neutral wire. Older motors can also leak electricity in to their motor housings. If the electricity is not returning through it's designed path then you may have a safety hazard and your GFCI is protecting you.
To test a tripping GFCI follow these steps.
1. Remove every appliance connected to the GFCI's circuit and then try to reset it. If the GFCI doesn't reset there may either be a wiring fault behind a socket outlet or your GFCI itself has become faulty.
2. Make sure what whatever you are plugging in to the GFCI is dry and not damaged.
3. Only plug in one item of electrical equipment at a time. If you are plugging in a defective item it will cause the GFCI to trip and that item should be replaced.
<><><>
From what this question is saying, the TEST button is doing its job - it is testing ( = checking) that the GFCI is working correctly!
After you have tested the device by pressing the TEST button you should be able to press the RESET button again - and DO NOT PRESS THE TEST button again - and everything should work.
Either your GFCI is bad [in which case replace it] or it is working perfectly.
<><><>
It is probably working. My sister had a similar problem. She just kept resetting until it held, but every time she got in her hot tub she got shocked.
Luckily she wasn't killed. It turned out to be the fly weights shorting out against the capacitor wires, turning the water into the hot leg. Don't mess around with this kind of problem.
<><><>
Another possible cause for tripping a GFCI is radio frequency energy. If you are close to a transmitting station this may occur. I have seen a GFCI trip when a car, equipped with a transmitter, pulled into a driveway and keyed up the transmitter. If the output is high enough and/or at a particular frequency, this may happen. If so, the GFCI(s) may need to be shielded.
<><><>
As always, if you are in doubt about what to do, the best advice anyone should give you is to call a licensed electrician to advise what work is needed.
Before you do any work yourself,
on electrical circuits, equipment or appliances,
always use a test meter to ensure the circuit is, in fact, de-energized.
IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOB
SAFELY AND COMPETENTLY
REFER THIS WORK TO QUALIFIED PROFESSIONALS.
Yes, a GFCI outlet can go bad and prevent power from coming through. If the GFCI outlet is faulty or has tripped, it can interrupt the flow of electricity to the entire circuit. In this case, replacing the GFCI outlet may be necessary to restore power to the affected area.
You can determine if an outlet is after a GFCI by pressing the "test" button on the GFCI outlet. If the GFCI trips and cuts off power to the outlet, then that outlet is downstream from the GFCI. If power is not cut off, then that outlet is upstream from the GFCI.
To change an outlet to a GFCI outlet, first turn off the power to the circuit at the breaker box. Remove the existing outlet and install the GFCI outlet following the manufacturer's instructions. Test the GFCI outlet to make sure it is working properly before using.
It is recommended to have GFCI protection for all electrical outlets in a garage to help reduce the risk of electric shocks. This would typically involve installing a GFCI outlet at the beginning of the circuit to protect the rest of the outlets downstream.
No, a GFCI outlet is designed for use with standard 120-volt circuits. Attempting to use a GFCI outlet with a 240-volt split circuit could cause damage to the outlet, the circuit, and could present a safety hazard. It is not recommended to use a GFCI outlet in this manner.
To determine if a GFCI outlet is bad, you can press the "test" and "reset" buttons on the outlet. If pressing the "test" button does not trip the outlet or pressing the "reset" button does not restore power, the GFCI outlet may be faulty and should be replaced.
To determine if a GFCI outlet is bad, you can press the "Test" and "Reset" buttons on the outlet. If pressing the "Test" button does not trip the outlet or pressing the "Reset" button does not restore power, the GFCI outlet may be faulty and should be replaced.
To determine if a GFCI outlet is bad, you can press the "test" and "reset" buttons on the outlet. If pressing the "test" button doesn't trip the outlet or pressing the "reset" button doesn't restore power, the GFCI outlet may be faulty and should be replaced.
To determine if a GFCI is bad, you can press the "test" and "reset" buttons on the outlet. If pressing the "test" button does not trip the outlet or pressing the "reset" button does not restore power, the GFCI may be faulty and should be replaced.
Signs of a bad GFCI outlet include tripping frequently, not resetting properly, or not providing power. To fix it, first try resetting the outlet. If that doesn't work, replace the outlet or seek professional help.
Yes, a GFCI outlet can go bad and prevent power from coming through. If the GFCI outlet is faulty or has tripped, it can interrupt the flow of electricity to the entire circuit. In this case, replacing the GFCI outlet may be necessary to restore power to the affected area.
No, except that you insert the wires into the holes on the back of the outlet. The power in connects to the LINE side of the outlet and power out connects to the LOAD side of the outlet. This is clearly marked on the back of the outlet. This will not only protect the outlet with the GFCI installed but all outlets receiving their power from that GFCI. If you do not want to protect the outlets receiving power from the outlet then connect that outgoing wire to the LINE side also. But know that only the outlet with the GFCI will be protected and all other outlets will not be GFCI protected.
No, a refrigerator does not typically need to be plugged into a GFCI outlet.
Is the GFCI test button stuck on your outlet?
To replace a GFCI outlet with a regular outlet, you will need to turn off the power to the outlet at the circuit breaker, remove the GFCI outlet from the wall, disconnect the wires from the GFCI outlet, and then connect those wires to the new regular outlet. Make sure to follow proper safety precautions and consult a professional if needed.
To properly wire a GFCI outlet to another outlet, you should connect the line wires from the power source to the line terminals on the GFCI outlet. Then, connect the load wires to the load terminals on the GFCI outlet. Make sure to follow the manufacturer's instructions and consult a professional electrician if needed.
Yes, a GFCI outlet can go bad over time due to wear and tear. You can tell if it needs to be replaced if it no longer trips when tested, if it fails to reset, or if it shows signs of physical damage or discoloration.