At 240 volts, and 7 amp current, you will have a load of 1680 watts (volts x amps = watts). A 2000 watt generator will sufice, however a 3500 watt generator, if within your budget, will power a few other necessities if required.

User Avatar

Wiki User

12y ago
This answer is:
User Avatar
More answers
User Avatar

AnswerBot

1w ago

To size a generator for a pump that draws 7 amps on each leg of a 240V circuit, you would calculate the total power consumption by multiplying the current (7A) by the voltage (240V) and the number of phases (2), which equals 3360 watts. Then, choose a generator with a rated power output greater than 3360 watts to ensure it can handle the load of the pump. A generator with at least a 4000-watt rating would be a suitable choice in this scenario.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How do you size a generator to operate a pump that draws 7 amps on each leg of a 240 Volt Circuit?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

Can you plug a 9000 BTU air conditioner unit into a 110-120 volt line safely?

Check and see what the amperage the A/C unit draws. These types of appliances should have their own dedicated circuit. If there is nothing of a high load on the existing 120 volt circuit and the A/C unit draws less than 12 amps, the unit should operate without tripping the breaker. If the A/C unit only has wattage and no amperage shown on the nameplate use this equation to find the amperage. I = W/E, Amps = Watts/Volts.


Can you wire a 120 volt ballast to a 347 volt circuit?

No, you cannot wire a 120 volt ballast to a 347 volt circuit. The ballast is designed to operate at a specific voltage, in this case 120 volts, and connecting it to a higher voltage circuit like 347 volts can damage the ballast and pose a safety hazard. It is important to match the voltage rating of the ballast to the circuit it will be connected to.


240 volt what is loop is it neutral?

A 240-volt circuit typically consists of two hot wires and a ground wire, with no neutral wire. The hot wires each carry 120 volts, while the ground wire is used for safety purposes. In a 240-volt circuit, the hot wires complete a loop by connecting to a load or device that requires the higher voltage to operate.


Why gen output of 220 volt increase too 400 volt?

If the output of a generator is increased from 220 volts to 400 volts, it could be due to an adjustment of the generator's voltage regulator or the generator being overloaded. This change in voltage could be dangerous for equipment designed to operate at lower voltages and could potentially lead to damage. It is important to ensure that the voltage output of a generator remains within safe limits for the equipment being powered.


Unit of measurement for electromotive force?

The unit of measurement for electromotive force (emf) is the volt (V). It represents the potential difference between two points in a circuit that causes current to flow. A voltage source such as a battery or generator can provide this electromotive force.

Related questions

Will a 208 volt 3 phase generator supply operate a 230 volt 3 phase motor?

Yes, but the motor's horsepower rating will not be reached.


Why won't a 230-460 volt motor work on a 120-208 volt circuit?

Because its designed to operate at 230-460, not 120-208.


Can your 30 amp generator pull a double 20 amp circuit?

When the term "double 20 amp circuit" is used, the presumption is that, it is 20 amps at 240 volts. If your generator has the breaker built in then, yes, you have the capacity to run 240 volt devices from your generator.


Can you plug a 9000 BTU air conditioner unit into a 110-120 volt line safely?

Check and see what the amperage the A/C unit draws. These types of appliances should have their own dedicated circuit. If there is nothing of a high load on the existing 120 volt circuit and the A/C unit draws less than 12 amps, the unit should operate without tripping the breaker. If the A/C unit only has wattage and no amperage shown on the nameplate use this equation to find the amperage. I = W/E, Amps = Watts/Volts.


Can you wire a 120 volt ballast to a 347 volt circuit?

No, you cannot wire a 120 volt ballast to a 347 volt circuit. The ballast is designed to operate at a specific voltage, in this case 120 volts, and connecting it to a higher voltage circuit like 347 volts can damage the ballast and pose a safety hazard. It is important to match the voltage rating of the ballast to the circuit it will be connected to.


How do you connect a volt to a circuit?

A volt can not be connected to a circuit.


Can 110v circuit power 240v devices?

You need a step-up transformer, to go from 110 to 220-240 volts. Then a 110 volt supply can operate 240 volt equipment.


How many amperes will a 28-volt generator be required to supply to a circuit containing five lamps?

It depends on how much power the lamps require, and on how they are connected.


What if my generator sends 120 volts and 65 amps into my 200 amp panel box will it run my well pump connected to a 20 amp 240 volt circuit?

No, the generator must output 220 volts which any generator I have ever seen does.


Can a 230 volt operate on 127 volt power?

No.


Will a 6000 watt generator power a machine that draws 14 amps?

Yes, Power (in watts) equals voltage times current (Amps). Amps = Watts/Volts If your generator is 6000 watts that would operate a 120 volt load up to 50 amps (6000/120=50). If you are running a motor or compressor, the initial inrush of current is about 3 times higher so 14 X 3 = 42amps. Should do fine...


Is 24 voltage a lot?

It depends on the use it is being put to. It is sufficient for a 24 volt circuit. Too much for a 12 volt circuit and too little for a 240 volt circuit.