In a residence assume you are referring to 120 volt supply. Watts = amps x volts x Power Factor. Now Power factor is one for resistive loads like incandescent light bulbs. Power Factor can vary from zero to one when inductive loads like motors are added. So the maximum theoretical wattage would be about 15 A x 120 V. However, you de-rate a breaker to 80% of capacity so as not to continually trip breaker. Therefore, the answer you are looking for in a practical sense is 120 x 15 x .8 = 1440 watts or 1.44 kilowatts.

User Avatar

Wiki User

14y ago
This answer is:
User Avatar
More answers
User Avatar

AnswerBot

6mo ago

A 15 amp breaker provides 1800 watts of power on a 120-volt circuit (15 amps x 120 volts = 1800 watts). It is important to note that exceeding this limit can result in tripping the breaker or causing damage to the electrical system.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: How many watts does a 15 amp breaker provide?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How many amp breaker is needed for 4000 watts at 220 volts?

The equation that you are looking for is I = W/E. Amps = Watts / Volts.


How many watts can a 20 amp breaker handle per hour?

A 20 amp breaker can handle up to 2400 watts per hour (20 amps x 120 volts = 2400 watts).


How many watts will a 30 amp two pole breaker handle at 240 volts?

30X240=7200


How many watts can be on a 15amp breaker?

At 120 volts a 15 amp breaker can be loaded to 1800 watts before it will trip. If it is a continuous load then the electrical code states that it is only allowed to be loaded to 80%. This will be 1800 x .8 = 1440 watts. If the voltage is not 120 volts use the following equation Watts = Amps x Volts. Amps being the breaker size that is to be used.


Can six recessed lights of 50 watts be on a 15 amp breaker?

Should be fine if that is all that is on the breaker.


How many watts will a 60 amp 2pole breaker handle?

A 60 amp 2-pole breaker can handle up to 14,400 watts (60 amps x 240 volts). This is because a 2-pole breaker provides 240 volts, which is the typical voltage for larger appliances and machinery.


How many watts can be put on a 20 amp 208 volt circuit breaker?

A 20 amp circuit breaker at 208 volts can handle up to 4160 watts (20 amps x 208 volts = 4160 watts). This is calculated by multiplying the amperage by the voltage to determine the maximum wattage capacity of the circuit.


If you have a 30 amp breaker how many watts can it use?

To answer this question a voltage must be given. Watts = Amps x Volts. <<>> Answer At 115 volts ac, 30 amps equals 3,450 watts.


20 amp breaker how many watts?

On a 20 amp breaker, you can safely operate devices that consume up to 2400 watts (20 amps x 120 volts = 2400 watts). Exceeding this limit can trip the breaker to prevent overheating and fire hazards.


Can a 15 amp breaker hold 300 watts at 120 volts?

Yes, it can.


What is the wire size required for 1800 watts for lamps?

14 gauge will handle it with a 15 amp breaker. If you use 12 gauge use a 20 amp breaker.


How many watts can a double 30 amp breaker switch handle?

The maximum wattage that a 30 amp breaker can handle is 30 x 230 = 6900 watts. Other variables come into play and this number will decrease depending on the load, duty time, and difference in voltage fluctuation.