The formulae for calculating watts to amps is Watts divided by Voltage. Therefore to get from Amps to Watts the calculation is Amps × Voltage. Therefore if you are working on a 240 volt supply the calculation is 20 (Amps) × 240 (Volts) which = 4800 watts.
Chat with our AI personalities
A 20 amp double pole breaker can handle a maximum of 4800 watts (20 amps x 240 volts = 4800 watts). This assumes a standard residential circuit with a voltage of 240 volts.
Each wire on a two pole 20 amp breaker will allow 20 amps maximum before the breaker will trip.
In a 20A double pole circuit breaker, although the breaker says 20A, the breaker is actually two 20A single pole breakers, joined together by one actuator.
A double pole circuit breaker has two 120v branch circuits, hence where the 240v comes from. The two are independent 120v circuits to ground. Each branch remains electrically independent of each other, but with one common ground. Each of the two branches, on these two single pole ‘joined’ breakers, will handle 20A, for a total of 40A.
For the more Technical:
Ohms law causes the joined breakers to behave as if it were a 40A circuit, as far as the electrical panel is concerned, because there’ll be 40A going into the breaker, but splitting into two separate 20A circuits, or branches, of electrical current: 20A+20A=40A.
Conclusion:
In the past, this was easy to see because, each side was labeled with the number 20; however, more and more manufacturers are electing to control both breakers in a 20A double pole circuit breaker, with one single handle.
Industrial Electronics, Computer Aided Design & Computer Aided Manufacturing
A 20 amp breaker can handle up to 2400 watts per hour (20 amps x 120 volts = 2400 watts).
30X240=7200
A 60 amp 2-pole breaker can handle up to 14,400 watts (60 amps x 240 volts). This is because a 2-pole breaker provides 240 volts, which is the typical voltage for larger appliances and machinery.
The load exceeds the limit of the breaker or fuse. For example a 20 amp breaker on a 120 volt circuit will handle 2400 watts. Exceed that wattage and the breaker will trip or the fuse will blow.
To answer this question a voltage must be given. Watts = Amps x Volts. <<>> Answer At 115 volts ac, 30 amps equals 3,450 watts.