answersLogoWhite

0


Best Answer

A 12 AWG wire would give you approximately 2.6 percent drop, which is less than the maximum allowable voltage drop. 14 AWG would drop you 10 volts (4.2 percent), which is still workable until you factor in the 80 percent design factor (i.e., you are only allowed to run a circuit at 80 percent of its design capacity).

If you REALLY need 15 amps, you have to design for 18.75 amps (which works out to a 14 AWG voltage drop of over 5 percent, which is not allowed), so you would need to use the larger wire (12 AWG) for a 3.3 percent drop.

User Avatar

Wiki User

βˆ™ 12y ago
This answer is:
User Avatar
More answers
User Avatar

AnswerBot

βˆ™ 4mo ago

For a 110 ft distance with a 220 volt 15 amp circuit, you would need to use at least 12-gauge wire to ensure efficient power transmission and to meet electrical code requirements. Thicker wire (e.g., 10-gauge) may be recommended for longer distances to minimize voltage drop and ensure safe operation. It's always a good idea to consult with a certified electrician for your specific needs.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 10y ago

More information is needed. The voltage and current that are required will have a significant effect on the wire size needed. In general a higher current requires thicker wire.

If the voltage is higher, e.g. 240 v instead of 120 v, the current drawn will be less for a given kilowatt load and that allows thinner wire.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 10y ago

First calculate the voltage drop allowed: 5% of 220 v is 11 v. Divide by the current to find the resistance: 11/25 is 0.44 ohms.

The total wire length is 500 ft or 152.4 metres so the resistance allowed per metre is 0.44/152.5 or 0.00288 ohms/m.

Copper wire of 1 mm2 is 0.0168 ohms per metre so the wire size required is a minimum of 0.0168/0.00288 mm2, which is 5.82 mm2. Therefore 6 mm2 cable should be used and this size of cable is a common one in Europe. The nearest suitable AWG size is #9 but #8 is probably commoner.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 16y ago

It is more important to know what the amps that are going to be required. That will determine what gauge wire to use.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What size wire for 110 ft 220 volt 15 amp?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Natural Sciences

How do you wire 220 volt from 2 110 volt lines. you have a concessions stand that is wired for 220 but everywhere you have been lately just keeps giving you 2 - 110 volt line?

To create a 220 volt connection using two 110 volt lines, you need to connect them in series. Ensure the two 110 volt lines are out of phase (provide opposite polarity) and then connect them together. This will result in a 220 volt supply for your concessions stand. It's important to consult a professional electrician to ensure proper wiring and safety.


Can you use a neutral wire from a existing 110 volt 20 amp circuit to supply a neutral for a washer dryer combo that has only a 220 volt 30 amp 2 wire?

No !


Can you use 110 volt printer with 220 volt?

No, you cannot use a 110-volt printer with a 220-volt power supply directly. The electrical requirements for the printer must match the power supply in order to function properly. Using the wrong voltage can damage the printer and pose safety hazards. You would need a voltage converter or a transformer to safely use a 110-volt printer with a 220-volt power outlet.


How do you change a 220 240 volt wire to a 110 120 volt wire?

To change a wire from 220-240 volts to 110-120 volts, you will need to reconfigure the wiring by connecting it to a transformer that steps down the voltage. This transformer will reduce the voltage from the higher range to the desired lower range, allowing you to safely use it with 110-120 volt systems. It's important to ensure the transformer is compatible with the current and wattage requirements of your device or equipment.


How can I install a 110 receptacle alongside a 220 receptacle using the 220 receptacle wires for power?

While you can physically do this it violates the Electrical Code. 110 Volt and 220 Volt receptacles are required by the Electrical Code to be on separate breakers for safety reasons, this would put them on the same 220 Volt breaker.

Related questions

How do you wire 220 volt from 2 110 volt lines. you have a concessions stand that is wired for 220 but everywhere you have been lately just keeps giving you 2 - 110 volt line?

To create a 220 volt connection using two 110 volt lines, you need to connect them in series. Ensure the two 110 volt lines are out of phase (provide opposite polarity) and then connect them together. This will result in a 220 volt supply for your concessions stand. It's important to consult a professional electrician to ensure proper wiring and safety.


What size wire for an 80 amp 220 volt circuit?

# 3 gauge


Can you use a neutral wire from a existing 110 volt 20 amp circuit to supply a neutral for a washer dryer combo that has only a 220 volt 30 amp 2 wire?

No !


Can you use Nintendo DSi on 110 volt and 220 volt?

no


Can you plug In a 220 volt to a 110 outlet?

no


Is France 110 volt or 220 volt?

France uses 220-240 volts for their electrical system.


Can you use a 220 volt printer on 110 volt service?

No, unless it is dual rated for 110 - 220 volt use. Check the manual or look at the rating sticker that should be somewhere on the printer.


Is a 220 volt electrical power wire the same as a 240 volt electrical power wire?

Yes 220 & 240 are considered the same.


How is 110 volts and 220 volts measured?

With a voltmeter Keep volt meter terminal on phase and neutral wire and it will show the exact volatage


What happens when a 110 volt breast pump is plugged in 220 volt outlet?

zzzzzzzzzzzAAAAAAAAAAAAAAAPPPPPPPPPP !!!!!


How do you wire a 220v dryer to run on 110?

You can't. A 220 volt dryer requires 220 volts in order to operate properly. It will not run on 110 volts.


Can you use 110 volt printer with 220 volt?

No, you cannot use a 110-volt printer with a 220-volt power supply directly. The electrical requirements for the printer must match the power supply in order to function properly. Using the wrong voltage can damage the printer and pose safety hazards. You would need a voltage converter or a transformer to safely use a 110-volt printer with a 220-volt power outlet.