0

A 12 AWG wire would give you approximately 2.6 percent drop, which is less than the maximum allowable voltage drop. 14 AWG would drop you 10 volts (4.2 percent), which is still workable until you factor in the 80 percent design factor (i.e., you are only allowed to run a circuit at 80 percent of its design capacity).

If you REALLY need 15 amps, you have to design for 18.75 amps (which works out to a 14 AWG voltage drop of over 5 percent, which is not allowed), so you would need to use the larger wire (12 AWG) for a 3.3 percent drop.

User Avatar

Wiki User

12y ago

What else can I help you with?

Continue Learning about Natural Sciences

How do you wire 220 volt from 2 110 volt lines. you have a concessions stand that is wired for 220 but everywhere you have been lately just keeps giving you 2 - 110 volt line?

To create a 220 volt connection using two 110 volt lines, you need to connect them in series. Ensure the two 110 volt lines are out of phase (provide opposite polarity) and then connect them together. This will result in a 220 volt supply for your concessions stand. It's important to consult a professional electrician to ensure proper wiring and safety.


Can you use a neutral wire from a existing 110 volt 20 amp circuit to supply a neutral for a washer dryer combo that has only a 220 volt 30 amp 2 wire?

No !


Can you use 110 volt printer with 220 volt?

No, you cannot use a 110-volt printer with a 220-volt power supply directly. The electrical requirements for the printer must match the power supply in order to function properly. Using the wrong voltage can damage the printer and pose safety hazards. You would need a voltage converter or a transformer to safely use a 110-volt printer with a 220-volt power outlet.


How can I install a 110 receptacle alongside a 220 receptacle using the 220 receptacle wires for power?

While you can physically do this it violates the Electrical Code. 110 Volt and 220 Volt receptacles are required by the Electrical Code to be on separate breakers for safety reasons, this would put them on the same 220 Volt breaker.


How do you change a 220 240 volt wire to a 110 120 volt wire?

To change a wire from 220-240 volts to 110-120 volts, you will need to reconfigure the wiring by connecting it to a transformer that steps down the voltage. This transformer will reduce the voltage from the higher range to the desired lower range, allowing you to safely use it with 110-120 volt systems. It's important to ensure the transformer is compatible with the current and wattage requirements of your device or equipment.

Related Questions

What is the recommended wire size for a 220 volt circuit according to the 220 volt wire size chart?

The recommended wire size for a 220 volt circuit according to the 220 volt wire size chart is typically 10 gauge wire for a circuit with a maximum of 30 amps.


What is the recommended wire size for a 220-volt electrical circuit?

The recommended wire size for a 220-volt electrical circuit is typically 10-gauge wire.


What is the recommended wire size for a 30 amp 220 volt circuit?

The recommended wire size for a 30 amp 220 volt circuit is typically 10 gauge wire.


What is the appropriate wire size for a 220 volt 30 amp circuit?

The appropriate wire size for a 220 volt 30 amp circuit is typically 10 gauge wire.


What is the appropriate wire size for a 220 volt circuit with a 30 amp capacity?

For a 220 volt circuit with a 30 amp capacity, the appropriate wire size would be 10 gauge wire.


What is the appropriate wire size for a 220 volt circuit with a 40 amp load?

For a 220 volt circuit with a 40 amp load, the appropriate wire size would be 8 AWG (American Wire Gauge) copper wire.


What size wire for an 80 amp 220 volt circuit?

# 3 gauge


How do you wire 220 volt from 2 110 volt lines. you have a concessions stand that is wired for 220 but everywhere you have been lately just keeps giving you 2 - 110 volt line?

To create a 220 volt connection using two 110 volt lines, you need to connect them in series. Ensure the two 110 volt lines are out of phase (provide opposite polarity) and then connect them together. This will result in a 220 volt supply for your concessions stand. It's important to consult a professional electrician to ensure proper wiring and safety.


Can you use a neutral wire from a existing 110 volt 20 amp circuit to supply a neutral for a washer dryer combo that has only a 220 volt 30 amp 2 wire?

No !


Can you use Nintendo DSi on 110 volt and 220 volt?

no


Can you plug In a 220 volt to a 110 outlet?

no


Is France 110 volt or 220 volt?

France uses 220-240 volts for their electrical system.