8800w/240v = 36.6 Amps Since at some point (Thanksgiving, etc) you may use this range for more than 3 hours straight, your wire size must be calculated at 125 percent of that number: 36.6A * 1.25 = 45.75 (rounded to 46) Amps Using the NEC table 310.16, 75 degree column, the smallest copper wire that can carry 46 amps is #8 AWG. If you use aluminum the smallest is #6 AWG.

User Avatar

Wiki User

16y ago

Still curious? Ask our experts.

Chat with our AI personalities

SteveSteve
Knowledge is a journey, you know? We'll get there.
Chat with Steve
TaigaTaiga
Every great hero faces trials, and you—yes, YOU—are no exception!
Chat with Taiga
ProfessorProfessor
I will give you the most educated answer.
Chat with Professor
More answers

For an 8800 watt stove operating on 240 volts, you would need a 40 amp circuit. The recommended wire size for a 40 amp circuit is typically 8 AWG copper wire. It is important to consult with a certified electrician to ensure proper installation and safety compliance.

User Avatar

AnswerBot

10mo ago
User Avatar

Technically it's a 20 amp load (20A x 240V = 4800W). However, you should not run a breaker at full load. The breaker is to protect the wiring from overheating and from short circuits. You should use 10 gauge wire and a 30 amp double pole breaker.

User Avatar

Wiki User

15y ago
User Avatar

Amps X Volts = Watts

Amps X 220 = 4,000

Amps = 18.181818181818...

You CAN get by with 12 AWG, and a 20 amp circuit, but that's really pushing it. Nothing else could be on the circuit and you'd be getting real close to the edge. The breaker would no doubt run warm and you'd probably get quite a number of "false trips".

It isn't that much more expense to use a 10 AWG wire and a 30 amp circuit, and it will save you a LOT of trouble in the future.

User Avatar

Wiki User

14y ago
User Avatar

First thing that has to be done is find the amperage as that is how the wire size is chosen. The formula you would use id I = W/E, Amps = Watts/Volts. 4500/220 = 20 amps.

A #10 copper conductor with an insulation factor of 75 or 90 degrees C are both rated at 30 amps. The heater conductor has to be de rated to 80% capacity so 30 x .8 = 24 amps. Your load amperage is only 20 amps so this conductor will be the right size.

User Avatar

Wiki User

12y ago
User Avatar

This heater probably runs on 240 volts, draws 20 amps, would require minimum 12 gauge wire, or 10 Ga wire depending on the length of the wire

User Avatar

Wiki User

15y ago
User Avatar

AWG # 10 with ground. Must be powered by a 30 amp breaker.