# 4 gauge THHN or THHW is rated for 95 amps and would normally be the correct wire size. However, at 300 ft. from the source, you definetely will have a substantial voltage drop. Therefore, you need to up the conductor size to # 3 gauge.

User Avatar

Wiki User

βˆ™ 15y ago
This answer is:
User Avatar
More answers
User Avatar

AnswerBot

βˆ™ 4mo ago

For a 240-volt 20-amp circuit running 300 feet, you should use at least a 10-gauge copper wire to prevent voltage drop over the distance. It is advisable to consult local electrical codes and consider factors like insulation type and installation method to ensure proper sizing and safety of the wiring.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 13y ago

12 AWG is the normal requirement for 20 A. At 300 ft. there is about 1/2 ohm resistance, so at full load of 20 A you would have a drop of 10 volts which shouldn't cause a problem under most conditions.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 10y ago

A 300 MCM copper conductor with an insulation factor of 90 degrees C is rated at 320 amps.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 13y ago

12/2 in Canada

<<>>

A #8 copper conductor will limit the voltage drop to 3% or less when supplying 20 amps for 120 feet on a 120 volt system.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What wire 240 volts 20 amps 300 feet?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What gauge wire would I need for 2500 feet for 240 volts and 0.4 amps?

A #14 wire will do the job.


What is ampere rating of 10 gauge wire at 120 volts and at 240 volts?

30 amps.


What size copper wire should you use for 240 volts 200 amps?

3/0 wire 3/0 wire


What size copper wire do you need for 240 volts 16 amps at 150ft?

10 gauge


How many amps can a 12 awg wire carry at 240 volts?

A 12 AWG wire is typically rated for 20 amps in standard household wiring. At 240 volts, this wire can safely carry up to 20 amps of current.


What wire 240 volts 6500 watts 100 ft?

The sizing of wire is calculated by the amount of current the circuit draws. To find the amperage when the wattage is known use the following formula, Amps = Watts/Volts. 6500/240 = 27 amps. A #10 AWG copper conductor will limit the voltage drop to 3% or less, when supplying 27 amps at 240 volts for a 100 foot distance.


What gauge wire would you need 5600 watts 240 volts 23.3 amps?

AWG # 10.


What size wire for 240 volts 200 amp service 200 feet away?

A 3/0 copper conductor will limit the voltage drop to 3% or less when supplying 200 amps for 200 feet on a 240 volt system.


How many amps does a 2000 watt heater draw at 240 volts?

Amps * Volts = Watts So, Watts / Volts = Amps 2000 / 240 = 8.333 Amps You should run the circuit on a two pole 15 Amp breaker, using 14 AWG, 2 conductor (plus ground) wire, just so you have a little safety factor in the circuit size.


What gauge wire for aluminum 240 volts 20 amp 200ft?

A #6 aluminum conductor will limit the voltage drop to 3% or less when supplying 20 amps for 200 feet on a 240 volt system.


How do you determine amperage service for a 240V single-phase three-wire system what formula do i follow?

You have to know the maximum amps you wish to deliver or draw of the device or devices you wish to power. There are charts on the internet for wire gauges and distance that you can follow. For example: A 12 gauge wire will handle 20 amps safely for runs up to 100 feet. You go down 1 gauge for runs over 100 feet. So if you are running 175 feet at 20 amps you should use 10 gauge so voltage drops don't occur. Voltage has no effect on rated current output other than selecting a wire or cable that is rated for the working voltages. 20 amps at 240 volts is the same as 20 amps at 120 volts. As long as the wire is rated at 240 volts, it will carry 20 amps at voltages less than 240 the same.


What gauge wire is required for 25 amps over 100 ft at 240 volts?

10 AWG copper.