That probably indicates a fault in the exhaust fan; either a motor winding has failed, or the fan is wired improperly.
Just to amplify - The Ground Fault Current/Circuit Interrupter (GFCI) detects current flowing to ground that should instead be flowing in the fan. This means somewhere in the fan the Hot wire has an unintended path to ground and is a shock hazard. You should check the wiring to the fan (with power off) and make sure there are no bare wires that could be causing your problem and if you don't see anything obvious you should replace the fan.
When a GFCI-protected extension cord is plugged into an outlet that is also GFCI protected, it provides an additional layer of protection against electric shock. Both devices work in conjunction to quickly detect any imbalance in the electrical current and trip the circuit if necessary. This redundancy helps ensure increased safety against electrical hazards.
GFCI receptacles are designed to trip at around 5 milliamps (0.005 amps) of current leakage to ground. When the GFCI detects this level of imbalance, it quickly shuts off the power to prevent electric shock.
A GFCI trips when it detects a difference in the amperage going to the outlet and what is coming back. Even 4-6 miliamps difference will trip the outlet.
A GFCI outlet will trip when it detects a ground fault, not when the current is simply reduced or shut off. The purpose of the GFCI outlet is to quickly shut off power when it senses a potential electrical hazard, such as a ground fault or leakage.
The electrical code exists to protect against three things... 1. shock 2. fire 3. idiots The purpose of a Ground Fault Current/Circuit Interrupter (GFCI) is to detect when there is an imbalance between the power going through the hot and neutral terminals. If one has more power going through it, that means that the power that was supposed to be going through the other is actually going through something else (ground fault or maybe even a person). If this happens when the fan is turned ON, it means that you have a ground fault (the ground is getting power instead of the fan). This happens whenever a powered wire touches anything that's grounded Check your GFCI receptacle and the fan's electrical wiring to make sure there is no way the white and black wires can touch anything metal other than their terminals. If this happens when the fan is turned OFF, the fan is probably still turning and, being attached to a motor, becomes a small generator. This EMF (Electro Magnetic Feedback) is probably the culprit causing the GFCI to trip. You'll need to ask an electrician about this scenario and they'll tell you the best solution depending on the problem.
To test a GFCI outlet, press the "Test" button on the outlet. This should trip the GFCI and cut off power to the outlet. To ensure it is functioning properly, plug in a device and press the "Reset" button. If the device turns on, the GFCI is working correctly.
Every time you trip the GFCI, the power to the device plugged into it will lose its supply voltage.
The GFCI (Ground Fault Circuit Interrupter) can trip with no load due to internal issues or a ground fault in the circuit. This can happen if there is a problem with the wiring or if the GFCI itself is faulty.
When a GFCI-protected extension cord is plugged into an outlet that is also GFCI protected, it provides an additional layer of protection against electric shock. Both devices work in conjunction to quickly detect any imbalance in the electrical current and trip the circuit if necessary. This redundancy helps ensure increased safety against electrical hazards.
GFCI receptacles are designed to trip at around 5 milliamps (0.005 amps) of current leakage to ground. When the GFCI detects this level of imbalance, it quickly shuts off the power to prevent electric shock.
A GFCI trips when it detects a difference in the amperage going to the outlet and what is coming back. Even 4-6 miliamps difference will trip the outlet.
The washer may trip the GFCI due to a ground fault, which means that electricity is flowing through an unintended path, potentially causing a safety hazard.
To check a GFCI breaker, press the "Test" button to trip it, then press the "Reset" button to restore power. Use a voltage tester to confirm that the power is off when the GFCI is tripped and on when it is reset. If the GFCI does not trip or reset properly, it may need to be replaced.
A GFCI can trip with no load on it due to internal issues, such as a faulty wiring connection or a malfunctioning internal component. This can cause the GFCI to detect a ground fault even when there is no actual fault present, leading to the tripping of the device.
A GFCI outlet will trip when it detects a ground fault, not when the current is simply reduced or shut off. The purpose of the GFCI outlet is to quickly shut off power when it senses a potential electrical hazard, such as a ground fault or leakage.
The electrical code exists to protect against three things... 1. shock 2. fire 3. idiots The purpose of a Ground Fault Current/Circuit Interrupter (GFCI) is to detect when there is an imbalance between the power going through the hot and neutral terminals. If one has more power going through it, that means that the power that was supposed to be going through the other is actually going through something else (ground fault or maybe even a person). If this happens when the fan is turned ON, it means that you have a ground fault (the ground is getting power instead of the fan). This happens whenever a powered wire touches anything that's grounded Check your GFCI receptacle and the fan's electrical wiring to make sure there is no way the white and black wires can touch anything metal other than their terminals. If this happens when the fan is turned OFF, the fan is probably still turning and, being attached to a motor, becomes a small generator. This EMF (Electro Magnetic Feedback) is probably the culprit causing the GFCI to trip. You'll need to ask an electrician about this scenario and they'll tell you the best solution depending on the problem.
GFCI Breakers are quite a bit more expensive than a GFCI outlet. More often than not a typical residence will need only a handful of GFCI outlets that combined together will be cheaper than a GFCI breaker. If you need to protect a series of outlets with GFCI protection you can simply connect the rest of the outlets on that same circuit downstream from the first outlet on the line and make that the GFCI. All you have to do is connect all the other outlets to the LOAD side of the GFCI outlet. If a GFCI fault occurs in any of the outlets down stream they will trip that very first GFCI plug you placed and keep you safe.