answersLogoWhite

0


Best Answer

The answer to that question depends on exactly where in the building's wiring is being asked about.

The only place the neutral and ground (or "earth") wires in a building should ever be tied (or "connected") together is at the incoming service main breaker panel "upstream" of all the fuses and/or circuit breakers which are there to protect the hot (or "live") wires for the various circuits installed in the building.

In the absence of an earth wire (= ground wire in US/Canadian English), if the appliance suffered some damage that caused a short circuit between the high voltage "hot" lead and the case of the appliance, the damage would make the case live and it would cause an electrical shock to anyone who touched it.

If the case is earthed by using a ground wire (= earth wire in British English), if that same damage occurred the hot lead would immediately be shorted to ground and in theory cause the fuse to blow or circuit breaker to open, thus eliminating the danger of a live case.

<><><>

In the USA I think we refer to what you are calling an "earth wire," as a GROUNDING CONDUCTOR, which in effect is a separate conductor which seems to be doing nothing but is in fact a protective wire. It is there, ready to take the current away to earth if it, or the body/frame of the electrical device it is connected-to, makes contact with any "hot" wire. [120 Volts mains power is carried in two current carrying conductors "hot" and "neutral".]

So, IF one of the "hot" conductors should contact the metal frame or housing - perhaps because the appliance got damaged by being dropped from a table, or similar accident - the third wire which is the "ground" or "earth" wire, which runs directly from the housing to the grounding [or earth bus] in the fuse or breaker panel, will in effect cause a short circuit which should blow the fuse or trip the breaker.

This third wire also guarantees a current path back to the load center where the fuse or circuit breaker protecting that circuit is located, in the event the hot wire should be in contact with the frame, but the other [neutral/return] conductor should happen to be cut, disconnected, or open.

The idea is to guarantee that if a part of the device should become "hot," which could be fatal to anyone who then came into contact with it, would trip/open the circuit protection device [fuse or breaker], turning off the flow of current to that circuit.

<><><>

All the neutral and ground (or "earth") wires in a building are tied or linked together at the incoming service main breaker panel. This is the only place they should ever be tied together because it is "upstream" of all the fuses and/or circuit breakers protecting the hot (or "live") wires for the various circuits installed in the building.

Warning: we must never assume that a neutral is safe to touch: it has to be checked with a voltmeter or a voltage indicator to be sure it is not "live". This is because a neutral wire is designed to carry current under normal circumstances.

So, if a neutral wire going back to the incoming main breaker panel has not been properly connected - or suffers a deliberate disconnection or some accidental damage which causes it to break - then it and any neutral wires connected to it further downstream will go live up to the break because of being connected to the downstream loads which still have hot feeds coming into them!

That is why we should never use a neutral as a substitute for a proper, separate, ground or "earth" wire.

<><><>

In addition to the above description it should also be mentioned that the presence of an earth wire allows a very sensitive safety device called a Ground Fault Circuit Interrupter (GFCI) to operate. It will cut off the power supply to the appliance even if a tiny current of a few thousandths of an Amp is detected flowing in the earth wire, which should normally carry no current at all.

In USA/Canada, and similar countries which use mains supplies running at 120 Volts 60 Hz to feed power sockets, it is probable that the latest designs of GFCIs which are fitted to all new wiring work actually operate in the same way as the RCDs described in the next paragraph, although they are still commonly called GFCIs.

In Europe, where 230 Volts, 50Hz mains supplies are standard in homes, offices, etc. such protective "trip" devices are called Residual Current Detectors (RCDs) because, in addition to being able to detect small earth leakage currents, they have the ability to detect very small differences between the currents flowing in the hot (or live) wire and the neutral wire. Such imbalances might be caused by minor damage to the appliance which allows a small current - known as a residual current - to leak to earth either via the user or via the earth wire (if one is connected) even though the appliance itself is still working. So using an RCD helps to prevent a serious shock hazard to users if ever the kind of minor damage occurs which, in the absence of an RCD, would cause the appliance's casing to become "hot" or live.

Thus RCDs give a very high level of safe operation even if no circuit breaker has tripped and no fuse has blown and the appliance appears to be working normally. (But it has really become unsafe!) Because of the enhanced protection they give to users of appliances the latest European wiring regulations (= wiring codes in US/Canada and elsewhere) make it compulsory to fit RCDs to all new power circuits.

<><><>

As always, if you are in doubt about what to do, the best advice anyone should give you is to call a licensed electrician to advise what work is needed.

Before you do any work yourself,

on electrical circuits, equipment or appliances,

always use a test meter to ensure the circuit is, in fact, de-energized.

IF YOU ARE NOT ALREADY SURE YOU CAN DO THIS JOB

SAFELY AND COMPETENTLY

REFER THIS WORK TO QUALIFIED PROFESSIONALS.

User Avatar

Wiki User

βˆ™ 13y ago
This answer is:
User Avatar
More answers
User Avatar

Joe Howard

Lvl 2
βˆ™ 3y ago

A comment about your statements re: GFCI receptacles.

A GFCi does NOT trip because of current on the ground path. It trips because it senses an inbalance of current between the hot & neutral wires. That inbalance MAY be caused by current flowing on the ground due to some sort of issue in the circuit wiring or the load. But the inbalance may be caused by current flowing ANYWHERE that is not on the hot and neutral, for instance through your body to ground. A GFCI does NOT monitor current on the ground wire. It only monitors the current on the hot and neutral to be equal within 3-4 thousands of an amp, a difference greater than that it trips. That is why GFCIs will work just fine on a 2 wire circuit (no ground). The handy GFCI testers will not work when a GFCI is on a 2 wire circuit because those testers direct some current from the hot and neutral circuit onto ground to cause an inbalance tripping the GFCI. No ground, no inbalance, thus tester doesn't work. BUT if you get an inbalance on a 2 wire circuit, that GFCI will work just fine.

This answer is:
User Avatar

User Avatar

Wiki User

βˆ™ 10y ago

No, they should not be wired together.

This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Should the ground and neutral wires be wired together?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Electrical Engineering

Does the neutral wire have a charge in a gfci circuit breaker?

No. Not if the GFCI is wired correctly. The neutral wire should always be cold, or at ground potential.


Will a GFI outlet keep tripping because it's line is wired to a fuse box panel where the neutral and ground are together?

No, that alone would not cause a GFCI to trip because that is the proper way to wire a panel.


On a standard three prong AC outlet what should the AC voltage measure between neutral and ground?

Zero, or very close to it. If there is a large neutral current flowing, voltage drop on the neutral leg could cause a volt or so to read between the two. If you read full line voltage, the outlet is wired wrong!


What can happen if a utility-sized electrical generator has an ungrounded neutral?

What you need to define is the statement "utility- sized electrical generator". It depends on what the generators output is used for as to the way it is internally wired. In some configurations there is no neutral to ground as in a Delta configuration.If the generator is configured for a Wye output and the neutral centre tap is not grounded there will be a floating voltage between the generator and the utility system ground. It is for this reason that the generator's neutral point is grounded to bring the floating voltage down to zero volts to ground.


Why is the neutral point grounded on a transformer?

The secondary side (output) of a three phase transformer develops a "separately derived system". That is why you do notsupply a neutral to a three phase transformer. It develops its own reference to ground by being bonded to the transformer casing and to a substantial earth ground, such as a ground rod. The XO tap on a transformer provides the neutral to the secondary line. It will have a double wire lug. The neutral wire going to the panel being supplied goes under one lug and the same size wire is to go to the ground lug on the transformer chassis The ground lug is also a double with the other lug to be wired to the earth ground.

Related questions

How do you wire for reversed polarity?

the hot and neutral are wired forwards the ground and neutral are wired backwards


Does the neutral wire have a charge in a gfci circuit breaker?

No. Not if the GFCI is wired correctly. The neutral wire should always be cold, or at ground potential.


Should the live and neutral wires be wired together?

No, live and neutral wires should never be directly wired together. They serve different purposes - live carries current to the appliance, while neutral returns current to the source. Mixing them up can cause electrical hazards and damage to the equipment.


How should old 3 wire stove be wired in panel bare wire to neutral or ground or both?

The bare wire from the old 3-wire stove should be connected to the grounding terminal in the panel. The neutral and ground should not be bonded together at the stove. If the stove requires a 4-wire connection, it's best to run a new 4-wire circuit to meet current electrical codes for safety.


Can the bare grounded neutral conductor of a service be buried directly in the ground?

No, the bare grounded neutral conductor of a service should not be buried directly in the ground. It should be installed above ground or within a suitable raceway or conduit to provide proper protection against damage or corrosion.


Neutral and hot wired backwards?

For a US 3-prong plug, a smaller slot should be hot, the longer slot should be neutral, and the screw that holds the plate on should be ground. Cheap, inexpensive testers are available at hardware stores.


Is the AC wide prong for hot or neutral?

The AC wide prong is the neutral. An AC voltmeter measuring from narrow prong to ground should show line voltage; measurement from wide prong to ground should show zero. In a two-conductor power cord (and some three-conductor cords), the ridged side should be the neutral. In any light-bulb socket, the outer ridge should be wired to neutral.


Single phase 4 pole Gen alt w 240V 60hz output no neutral. you check from each lead to ground and get 50-70V How do you get a neutral for connecting Gen to a standard breaker box having 240V and 120V?

If the generator does not have a neutral wire, one option is to create a artificial neutral by bonding one of the hot wires to ground. This should only be done if the generator is designed for this application and in line with local electrical codes. It is recommended to consult with a qualified electrician to ensure this is done safely and in compliance with regulations.


Will a GFI outlet keep tripping because it's line is wired to a fuse box panel where the neutral and ground are together?

No, that alone would not cause a GFCI to trip because that is the proper way to wire a panel.


Is it OK illegal or dangerous to connect the neutral to ground to make the circuit work?

Connecting the neutral and ground wires in a circuit is dangerous and against electrical code because it can create a hazardous condition known as a ground fault. This can lead to electric shock, fires, and damage to equipment. It is important to keep the neutral and ground wires separate to ensure the safety and integrity of the electrical system.


On a standard three prong AC outlet what should the AC voltage measure between neutral and ground?

Zero, or very close to it. If there is a large neutral current flowing, voltage drop on the neutral leg could cause a volt or so to read between the two. If you read full line voltage, the outlet is wired wrong!


Is the ridged wire neutral or hot?

If wired properly the ridged wire is the neutral.