Yes. I am assuming this is a residential question.

A better answer is...if the 8 recessed lights draw fewer than 16 amps together, it is good.

User Avatar

Wiki User

12y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Can 20 amp breaker with 12 gauge wire handle 8 recessed lights?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

Can a 20 amp breaker with 12 gauge wire be used for recessed lighting?

Yes. In the US at least.


What is the wire size required for 1800 watts for lamps?

14 gauge will handle it with a 15 amp breaker. If you use 12 gauge use a 20 amp breaker.


Can you use 14 gauge wire with a 15 amp breaker for recessed lighting?

To answer this question the circuits voltage must be stated. Find the total wattage of the lights, use the following formula. I = W/E, where W is the total wattage and E is the circuit's voltage.


Can you connect 14 gauge wire to 12 gauge wire on a 20 amp breaker if the 14 gauge is the end of the run and dedicated to lights?

yesAnother (corrected) answer.NO! The circuit breaker is there to protect the wiring from overheating. It wouldn't matter where on the circuit you decided to put the 14 gauge wire, you would need to change the breaker to 15 Amp if you did that. Using 14 gauge wire on a 20 amp circuit is a fire hazard and contrary to UBC. Contact your local building and zoning department to verify.


If a 1950 era house has 10 gauge wiring for lights and outlets can you safely extend wiring with 12-2 for additional lights and outlets?

You can provided the protecting breaker for the circuit is 20 Amps or less.


What Size breaker for 6 gauge wire?

You need a 60 amp breaker.


How many amps will 4 gauge wire handle?

The amps that a four gauge wire will handle will depend with the thickness of the wire. If the wire is thin, the four gauge will handle 95 amps.


Can 13 gauge wire be connected to a 20 amp breaker?

No, because NEC says that 12 AWG wire is the smallest wire that can safely handle 20 A. If you installed a smaller wire on a 20 A breaker you could possibly overheat the wire and cause it to fail, which can start a fire. It would not be to code. And the National Electrical code does not list a 13 gauge wire.


What size wire for 28 amps?

Minimum size is 10 gauge with a 30 amp breaker. To be safe I would install an 8 gauge with a 40 amp breaker.


The voltage in one part of the house drops and in another part surges also lights dim here brighten there heaters etc won't work Other times all is fine When it occurs its on all circuits Help?

Does it surge past 120?? Drops are due too the fact that there are too many outlets or devices on one line. Trace the line that you have a voltage drop in and find which breaker it is, if the line that comes off the breaker is a 12 gauge wire and the breaker is a 15amp breaker you can put in a 20amp breaker. If the line is a 14 gauge line then you must leave the 15amp breaker in place and remove a device from it.


Can you use 14-3 wire on a 20amp breaker?

No. A 20 amp breaker needs 12 gauge wire.


What size breaker should be used on a 20 amp motor?

30 amp breaker with #10 gauge copper wire