answersLogoWhite

0


Best Answer

You can't "change" the outlet to a 30 amp.

The major limitation is the size of wire that feeds the outlet. A 15 amp circuit is typically run with 14 AWG wire. A 30 amp circuit must use 10 AWG wire.

To add a 30 amp circuit you'll need to run a new wire, new outlet and connect it all to a new breaker.

Always seek the services of a qualified electrician to make those kinds of changes. A mistake can lead to electrical fires and possibly death of someone in the home.

User Avatar

Wiki User

13y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Can you change a 120v 15 amp outlet into a 30 amp?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

Can you convert an old 15 amp 125 volt electrical outlet to a household electrical outlet?

A 15 amp 125 volt outlet is a household outlet.


Can you convert a 30 amp 120V RV receptacle into a normal 120V outlet?

You can, but your circuit will be "protected" by a 30 amp breaker. So you'll have to consider the safety issues of having wiring and appliances that can draw up to 30 amps before tripping the breaker. Will the wiring and circuity support that much current without damage? If not, then switch to a 15 or 20 amp breaker.


What amp plug does the average router have?

15 amp outlet on a 20 amp circuit.


What breaker to use in a bedroom that holds up to 15 amps with 120v?

15 amp breaker.


Can you tap into a 40 amp electric range outlet for a 15 or 20 amp wall outlet?

no. the breaker is 40amps.fire hazard


Can you use a 20 amp fuse and wire rated for it in a 15 amp outlet?

You can use the wire rated for 20 amps on a 15 amp receptacle but you can not use a 20 amp fuse on any device rated at 15 amps. This is a tricky part of the code about receptacle outlets, You can use a 15 amp duplex outlet on a 20 amp circuit. (duplex outlet two devices can plug in) If it is a single outlet then the outlet must be rated 20 amp. NEC table210.21(B)(3). ============ A 15 amp duplex receptacle can be wired to a 20 amp rated circuit. This means the breaker OR fuse protecting the circuit can be rated 20 amps if the wire is also rated at 20 amps (12 AWG). --Sparkfighter


What is the most common electricity outlet?

In North America the most common electricity outlet is 15 amp.


Can you change a 50 amp receptacle to a 15 amp receptacle?

Yes as long as you change the 50 amp breaker to a 15 amp breaker. You will be hard pressed to get the 50 amp #6 wire under the terminals of the 15 amp receptacle.


Is a 15 amp double tandem the same as a double pole 30 amp?

No the outlet holes are in parallel so the total ampacity of the receptacle is still 15 amps.


How many outlets can run off 1 gfi outlet?

Eight on a 15 amp circuit, tweleve on a 20 amp circuit, including the gfci receptacle itself.


What is the electrical formula to for calculating the number of 15 amp recepticles that can be install on a 15 amp circuit?

There isn't a formula, but the general rule is that you allow for 1 amp per outlet and you load the circuit to 80% of maximum. For a 15 Amp circuit you can have a maximum of 12 outlets.


An ordinary outlet should be calculated what?

For a home, to calculate the amount of receptacle outlets on a 15 amp circuit, each receptacle outlet should be calculated as not drawing more than one amp each.