Best Answer

There's something wrong here. 3250 watts on 240 volts is only 13.5 amps, not 40. And that would be 12 gauge wire on a 20 amp circuit. But that seems low for an oven. If it truly is a 40 amp appliance then the gauge would be #8 wire. The wiring info that comes with the appliance should tell you everything you need to know.

User Avatar

Wiki User

8y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What gauge wire to run 3250 watts 240 volts 60 feet along 40 amp circuit for oven in residence?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

How do you measur ampere?

You use an "amp gauge" to measure amps in an actual circuit. It is hooked in series with the load. It can be placed anywhere in the circuit as long as it is hooked in series. Mathematically, you have to know the resistance, or wattage and voltage of a circuit. Volts=amps*resistance or amps=volts/resistance, or resistance=volts/amps. Ohms law!


How many volts is 2 gauge 200 amp 3 ohms?

Ohm's Law states Volts = Amps x Resistance. You would need to apply 600 volts across 3 ohm load to have 200 Amps flow in circuit. Not sure what you are really asking and why you mentioned 2 gauge.


What is the typical number of amps per circuit and what is the typical number of volts that enter your home and what is the typical number of volts for each circuit and what is a gfi?

15 amps per circuit 240 Volts total 120 Volts each circuit GFCI=Ground Fault Circuit Interrupter


What gauge cable to run 240 volts?

The voltage has nothing to do with the gauge of wire needed to supply a given circuit. The size wire is determined by the amperage of the overcurrent protection device (circuit breaker, etc.) being used to supply power to the circuit.


Reducing the current you a circuit causes what?

Reducing the current to a circuit causes a higher resistance -- assuming constant Volts. Also, reducing the current to a circuit causes lower Volts -- assuming constant resistance.AnswerAltering the current has absolutely no effect on a circuit's resistance. Reducing the current will reduce line losses (I2R) and reduce the voltage drop along a conductor.


What does trouble code p0138 on 2001 dodge 1500 mean?

Downstream O2 sensor circuit volts high.Downstream O2 sensor circuit volts high.


How do you check the volts?

by attatching a voltmeter into the circuit you are trying to measure the volts of.


What is ampere rating of 10 gauge wire at 120 volts and at 240 volts?

30 amps.


A circuit has an applied voltage of 100 volts and a resistance of 1000 ohms What is the current flow in the circuit?

A circuit has an applied voltage of 100 volts and a resistance of 1000 ohms. The current flow in the circuit is 100v/1000ohms which would equal .1.


What do you need for a simple circuit?

volts current ohms


What measures the potential difference of a circuit in volts?

voltmeters


On 110 volts circuit the ground is normally?

green