answersLogoWhite

0


Best Answer

A #1 copper or 1/0 aluminium conductor will limit the voltage drop to 3% or less when supplying 100 amps for 100 feet on a 240 volt a single phase system.

User Avatar

Wiki User

7y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What re size for a 220 volt 100 amp panel distance d 100 feet?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

Are you 380 volt panel what size cable use?

With out knowing the amperage rating of the panel, an answer can not be given.


What size aluminum wire to feed 125 Amps 220 volt a distance of 175' and what size ground?

A 3/0 aluminum conductor will limit the voltage drop to3% or less when supplying 125 amps for 175 feet on a 220 volt system. If the 125 amp load is a sub distribution panel that is not going to be fully loaded to 125 amps then using the exact connected load, which might be smaller than 125 amps will effect the wire sizing. The grounding conductor for that size distribution panel is #6 bare copper.


What is the start up amps on a 200 hp 3 phase 480 volt motor?

i have 200 hp motor what i need cable size in 100 feet distance


What size wire for 30 amp breaker 240 volts 100 feet?

That distance you are going to have to install a sub-panel and run AWG # 4 wire and even then you will have a voltage drop of 7.45 volts giving you 232.55 volts at the sub-panel which is acceptable.


What is the minimum allowable side distance from 480 volt electrical panel and emergency safety shower?

30 inches


What AWG cable for 200' x 208 volt three phase 250 amp circuit?

A wire size of 250 MCM will limit the voltage drop to 3% over a distance of 200 feet.


What size of panel needed to charge a 12 v 35 amp battery for 13 hours?

What is the Solar panel wattage to use charging a 12 volt 45 amp battery.


What size wire for 110 volt 20 amp circuit 250 ft?

A #4 copper conductor will limit the voltage drop to 3% or less when supplying 20 amps for a distance of 250 feet at 120 volts.


What size wire do you use and do you need a 240 volt sub panel to send power to some lights and a 1500 watt 120 volt heater about 400 feet away?

If you want to be a indoor grower like your self you do stupid shite like ask these questions i a hope you have bond money PS spelling is wrong purposely


Can 220 volt be the source at the panel and 120 volt out from the panel?

No, the source voltage can not change to a lower voltage without using equipment to do so.


What is the wire size for 50 feet distance 120 volts 12 amps?

It depends on whether this is residential or commercial.Commercial has to be 12 guage in conduit.


What size wire for a 100 amp sub panel 40 ft away?

A #1 copper conductor is rated at 140 amps with an insulation rating factor of 90 degrees C at 240 volt single phase, will give you a full 100 amps at 200 feet. #4 wire should give you 95 amps. Anything over 200 feet you will start loosing more amps.