answersLogoWhite

0


Best Answer

50 amp breaker wired with AWG # 6 wire.

User Avatar

Wiki User

10y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What size breaker should be used for a double oven?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What size breaker should be used for a 3.6 kW oven?

3000 / 240 = Amps. You de-rate a breaker by 20 % for continuous load like an oven. You could get by with a 20 Amp breaker and 12 AWG wire. However, I would recommend 30 Amps and 10 AWG for an oven for the long run.


Will the Maytag Gas double oven fit in a built in space that currently has a regular standard oven?

Majority of the Maytag double oven (gas) should fit into a space built for a regular standard oven (gas) except for one or two larger size Maytag double oven(gas).


What size breaker do you need for 5.7kw neff oven?

A breaker is sized by the wire size. The wire is sized by the amperage. The formula for amperage is I = W/E. Amps = Watts/Volts. As you can see with no voltage stated an answer can not be given.


What size breaker should you use for a tnia-10 wire?

25 amp breaker


How do you calculate amp of circuit breaker to use on a 4800w oven?

Ovens typically run at 240 volts which will be a two pole breaker in your panel. Watts = volts x amps. 4800 / 240 = 20 amps. If by chance you are using 120 volts then double it to 40 amps. All wiring must conform to size of breaker used.


What size wire for 75 feet of wire for a 30 amp 220 volt oven?

A 30 amp breaker run 75 feet would require you use AWG #10 wire. But, an oven normally pulls more that 30 amps and I would not use #10 wire on a 30 amp breaker for an oven. Normally any newer oven is wired with AWG #6 gauge wire on a 50 amp circuit breaker so the breaker will not trip during heavy use of the oven. Some older ovens could use a #8 wire on a 40 amp breaker.


What size oven is needed for a 20lb turkey?

About 30' wide is the oven size recommended for a 20 lb. turkey. This oven can be a free standing, free standing double, or slide-in model.


When installing a circuit breaker do you size the breaker to correct wire size or the device its controlling?

When installing a circuit breaker, you size the breaker based on the wire size. The breaker should be matched to the ampacity of the wire to ensure proper protection against overloads and short circuits. The device being controlled by the breaker is not a determining factor in sizing the breaker.


How are Branch circuit protected?

Branch circuits are protected by the circuit breaker found in the electrical panel. Each circuit should have its one breaker. The breaker should be rated to protect the insulation of the wire, so you can determine the breaker size based on the circuit conductor size Example #14-2 should be protected by a 15 amp breaker


What size breaker should be used for a TNIA-10 wire?

running wire 12-2 300ft w/9ea. 27watt lights what size breaker should be used


What size wire and circuit breaker is needed for an electric oven 4 wires with rated load of 34.9 amps 220v that is about 100 foot run from the electrical panel?

That would be a 40 amp 220v circuit. Circuit breaker is 40 amps and wire is 8 awg. Should use solid copper wire. Follow oven installation instructions.


What type of ovens does NEFF provide?

NEFFs oven product line includes single and double ovens. They have 21 different single ovens and 14 double ovens. Each oven varies in terms of specs. The double ovens provide a bottom (Main oven) and a half size top oven.