Best Answer

A three phase 30 HP at 240 volts draws 80 amps. Motor feeders have to be rated at 125% of the motors full load amps. 80 x 125% = 100 amps.

A #

3 copper conductor with an insulation factor of 75 or 90 degrees C are rated at 100 and 105 amps respectively.

Non-time delay fusing is 225 amps, time delay fusing is 125 amps and a circuit breaker is sized by 250% x 80, the full load amps, which equals 200 amps.

User Avatar

Wiki User

11y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: What size wire and breaker for a 30 hp 240 volt 3 phrase motor?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Related questions

What is breaker size for 240 volt 9 KW?

The formula you are looking for is I = W/E.


What size breaker for a 208 volt single phase motor that pulls 1.4 amps?

208 volts is not a common single phase voltage but you could just size your breaker to the capabilities of the conductor. 208 is normally a phase to phase voltage <<>> Many 230 volt motors can be connected to lower voltage supplies. These motors can be connected to supplies of 208 and 200 volts. The code requirement is that the 230 volt full load amperage of the motor be increased by 10% and 15% respectively for wire sizing and breaker selection. To answer the question you will need a two pole 15 amp breaker.


How many amp circuit breaker for 3 hp 230 volt motor?

16A


What size breaker for a 1500 watt 120 volt heater?

15 amp


Can i wire a 7.2 volt motor up to a 18 volt battery will it just burn the motor out?

you can but if you do, you will/might: A) kill the motor,B)overload your 18 volt power supply, and C) maybe short a breaker if your power supply is also an ac to dc converter


What is the breaker size for a 10 KVA electric heater?

What size breakers are needed for a 30kva transformer 208 volt feed 600 volt out put


How many amps is a 3 hp 240 volt motor use?

AWG #10 copper on a 30 amp breaker.


You are putting in a 240 volt 4000 watt heater in a room what size breaker do you need?

20 amp


What size breaker for a 12 Volt 50 watt light?

50W@12V is 4.2 amps, so any breaker rated that or higher should work.


What size battery do you need for a 4.5 volt DC motor?

4.5 volt battery sold only in Russo


What size breaker for 120 volt 2500 watt water heater?

20 amp is perfect, 15 is fine


What size breaker should be used for 1500 watt bathroom exhaust fan heater?

20 amp breaker 12 gauge wire assuming its 120 volt