Best Answer

Not unless you change the wiring for that circuit. The breaker protects the wiring and if you install a 40 amp breaker on a 15 amp wire circuit you will have a fire in your home.

User Avatar

Wiki User

10y ago
This answer is:
User Avatar

Add your answer:

Earn +20 pts
Q: Can you upgrade a 15 Amps circuit breaker for a 40 Amp for a 8.5 Watt shower?
Write your answer...
Submit
Still have questions?
magnify glass
imp
Continue Learning about Electrical Engineering

What is making capacity of a circuit breaker?

Hard to define... A four year old child has the strength to physically "make" a typical household circuit breaker, while a teen would be able to "make" a typical industrial circuit breaker. (The latter breaker being physically much larger than the former.) Circuit breakers have their "breaking capacity" rated in AMPS. A typical household breaker is rated at 20, 30 or 50 Amps. Industrial breakers might be rated at 500 amps or a thousand or even more. Hope this helps but if it didn't answer your question, please rephrase it and ask again.


What size circut breaker for 10-2 wire?

A #10 wire has the capacity for 30 amps. No breaker larger than 30 amps should be used to protect the circuit.


What size amp circuit breaker should be used for a geyser?

Depends on how many amps it pulls and the size of the wire in the circuit.


What breaker for 17.3 amps?

I would suggest a 20 amp breaker. * Added - I would suggest a 25 amp breaker. A slight surge, depending upon what equipment is the source of the 17.3 amp load, should not result in circuit breaker opening. <<>> In North America, the electrical code only allows circuit loading up to 80% on a continuous load. A 20 amp breaker can be legally loaded to 16 amps. A 25 amp breaker can be legally loaded to 20 amps.


Should 25 amps breaker be replaced by 20 amps?

For typical residential house wiring 12 AWG wire is required for a 20 Amp breaker. If you change out the breaker for a 25 A breaker you would have to rewire the circuit with 10 AWG. In that case you could up the breaker to 30 Amps. All outlets and switches should be rated at the same voltage and current as the breaker.

Related questions

How can a 30 Amps fuse for a shower of 9.5KW be replace with a 40 Amps fuse on RCD trip?

If the current safety requirement is 30 amps, you can;t run if off of a larger circuit breaker. It violates NEC and is very unsafe. If the current requirement is 40 amps , it will continuously trip a 30 amp breaker because it is too small of a breaker in electrical requirement.


The Function Of A Twenty Amp Breaker?

It limits the current to the circuit at 20 Amps. If a load on the circuit draws more than 20 Amps the breaker will trip and interrupt the current to all devices on the circuit.


What is 6InA in circuit breaker?

61 nano-amps is 0.061 milliamps or 0.000061 amps


What is KA in Circuit Breaker?

KA stands for kilo-amps, or thousands of amps. Thus a 2KA breaker means it will trip when the load exceeds 2,000 amps.


What is the continuous current draw on a 20 amp circuit breaker?

The continuous current draw on a 20 amp circuit breaker should not exceed 16 amps to allow for a safety margin. This helps prevent overheating and potential tripping of the circuit breaker. It is important to follow the manufacturer's guidelines and not overload the circuit.


What size fuse required to supply a continuous load of 32 amps?

80% of 40 = 32 amps Load the circuit breaker to 80% choose a conductor to suit the circuit Breaker min.


If an electrician have a circuit that pulls a load of 10 amps what size breaker must that circuit be protected by?

For a circuit with a load of 10 amps, a breaker of 15 amps should be used for adequate protection. It is important to choose a breaker size that is slightly higher than the load to prevent frequent tripping and ensure safety.


What circuit breaker rating do you need for a 3 phase electric motor?

The circuit breaker is sized to the full load amps of the motor times 250%.


What would happenif you put an 8 amp circuit-breaker in a power circuit?

If you put an 8 amp circuit-breaker in a power circuit that draws more than 8 amps, the circuit-breaker would trip or disconnect the circuit to prevent overheating and potential fire hazards. It is important to always use the correct amperage rating for circuit-breakers to ensure safe operation of electrical circuits.


How many amps would it take to kick a 15 amp breaker with 7 ohms resistance on a 277 volt circuit?

A 15 amp circuit breaker should trip at 15 amps regardless of the load voltages or impedances. If you have 277 volts and 7 ohms, the current would be 39.5 amps and a 15 amp circuit breaker should trip.


What circuit breaker to install for 10 amp 250 volt circuit?

For a 10 amp, 250 volt circuit, you should install a circuit breaker rated for at least 10 amps and 250 volts. A common option would be a single-pole, 10 amp circuit breaker designed for 240-250 volt applications. Be sure to check the specifications and compatibility with your specific electrical panel.


What is the standard to select circuit breaker?

Add up your amps to calculate your breaker size. Add up your loads (amps), divide by 0.8, and choose that size breaker. If that number does not correspond to a standard size breaker you go to the next higher standard size breaker.