0

Not unless the wire going to the refrigerator outlet is AWG 10/2. If it is wired with 12/2 wire then you must use a 20 amp breaker. Using a 30 amp breaker is dangerous and a fire hazard.

User Avatar

Wiki User

12y ago

What else can I help you with?

Related Questions

What is the recommended amperage for a breaker to use with a 30 amp dryer?

The recommended amperage for a breaker to use with a 30 amp dryer is 30 amps.


Have 110volt refrigerator on a 30 amp breaker is that right?

No, a 110-volt refrigerator on a 30 amp breaker is not correct. A typical home refrigerator operates on a 15-20 amp circuit. A 30 amp breaker is typically used for larger appliances or equipment that require more power. Plugging a refrigerator into a 30 amp breaker may pose a safety hazard.


What is the appropriate double pole 30 amp breaker to use for a dryer installation?

The appropriate double pole 30 amp breaker to use for a dryer installation is a 30 amp double pole circuit breaker.


What breaker do you use for 10 2 wire?

Use a 30 amp breaker.


What size breaker can you use on a 7500watt generator?

Depends on the wire size you are using. If the generator breaker is a 30 amp then install a 30 amp breaker.


How do you turn a 30 amp circuit into a 15 amp cicuit?

Replace the 30 Amp Breaker with a 15 Amp breaker.


Is the 30 amp breaker for a motorhome the same as for a house?

Yes, a 30 amp breaker is a 30 amp breaker. It must however be able to fit the box it is installed in.


Can you use 10 gauge wire to connect a 2 15 amp outlets to a 30 amp breaker?

No, it is not safe to use 10 gauge wire with a 30 amp breaker as the wire is not rated for that high of a current. It is important to use the correct wire gauge that matches the breaker amperage to prevent overheating and potential fire hazards. For a 30 amp breaker, you should use at least 10 gauge wire.


Can you use a 20 amp circuit breaker for an electric dryer?

If you are referring to a cloths dryer, the answer depends on the requirements of the dryer. Most dryers require AWG#10 wire with a 30 amp fuse. If the wiring is AWG#12 then use a 20 amp breaker but never use it on AWG#10 which requires a 30 amp breaker. If you are referring to a hair dryer then yes a 20 amp breaker is fine.


Is a 40 amp circuit breaker ok for a 30 amp air conditioner?

No, it is not recommended to have a circuit breaker with a higher amperage rating than the device it is protecting. In this case, you should use a 30 amp circuit breaker for a 30 amp air conditioner to ensure proper protection from overcurrent.


What is the recommended amperage for an RV breaker, specifically for a 30 amp RV breaker?

The recommended amperage for a 30 amp RV breaker is 30 amps.


What is the maximum amperage capacity of a 30 amp breaker?

The maximum amperage capacity of a 30 amp breaker is 30 amps.