answersLogoWhite

0

You would need to know how FAR the load is from the service point. Then use an online calculator or the voltage-drop formula to determine the minimum diameter of the conductors necessary to provide 95 percent of the supply voltage to the device at the other end.

<<>>

If distance is not a factor, the wire size is determined by the amperage the wire has to carry. Using the formula I = W/E, Amps = Watts/Volts = 3000/380 = 7.98 amps.

A #14 copper conductor with an insulation factor of 75 or 90 degrees C is rated at 15 amps. This size wire has nearly double the capacity that you need.

User Avatar

Wiki User

12y ago

What else can I help you with?

Continue Learning about Electrical Engineering
Related Questions

Are you 380 volt panel what size cable use?

With out knowing the amperage rating of the panel, an answer can not be given.


Can you run 480 volt motors in a 380 volt system?

Can I run 480 volt , 60 HZ motor at a 380 volt , 60 Hz system?


How do you get a 220 volt single phase from 380 volt 3phase synchrounos generator?

220 volt single phase from 480 volt 3 phase that one wire taken one phase and second wire connected in earth point. we get 220 v The above answer is incorrect, one phase from a three phase 480 volt system will give you 277 volts to ground. You must use a transformer to get the voltage you need.


Can you run 220 volt motor compressor a 380 volt supply using power inverter?

No 380 volts is too wide a spread to use a 220 volt motor on.


How do you get a 380 volt 3 phase motor to run on a 220 volt 3 phase power source?

Use a transformer.


Can you collect one 220 volt phase from a 380 volt three phase plug?

Answer for UK and countries running a 50 Hz supply service.The voltage potential of 380 volts is not common to North America.It will probably be difficult to tap into the plug to get the voltage.If you have a three phase 380 volt supply from a source then you can obtain a single phase voltage of 220 volts from it. 220/380 is a wye voltage connection. 380 divided by 1.73 will give you 220 volts. L1 - N = 220V, L2 - N =220V, L3 - N = 220V. L1 - L2 = 380, L2 - L3=380, L3 - L1 = 380.


How do you get 380 volt from 220 3 phase?

Only with a 3 phase transformer.


What power is a 380 amp car battery in volts?

It will be a 12 volt battery.


What gauge wire do you need for 110 volt one third HP 190 feet from breaker box?

For a 190 feet distance for a 110 volt, one third HP motor, you would need at least a 14-gauge wire to ensure efficiency and safety of the electrical system. It is important to consult with a qualified electrician to ensure proper wire size based on the specific requirements of the motor and installation conditions.


Where would you find 380 volt being used?

380 volt is commonly used in industrial settings for heavy machinery, commercial buildings for air conditioning systems, and in some residential buildings for large appliances like electric stoves.


How connect a transformer 380 volt 3 pH to 220 volt mono pH?

any one of the three line to neutral is 220 volts


What size bullet does a Lorin 380 use?

9x17mm, otherwise known as the .380 ACP.