Yes but you will not get the full watt rating out of the tank. Watts = amps x volts. Say the tank draws 20 amps. 20A x 240V = 4800 watts. 20A x 208V = 4160 watts. It will take longer to heat your water with less wattage.
Watts = Current x Volts with your resistive heat application. To figure out resistance you need to know voltage and current. Since you are drawing 6 amps then Volts = 325/6. This means that there is about 54 volts supplying the heater which seems like a very strange supply voltage. Since Volts = Current x Resistance the resistance = 325/36.
about 4800 watt but should not use it 100% so to be safe 4000 watt (80%)
Each baseboard heater will draw a little over 4 amps at 120 volts or 2 Amps at 240 volts. The total number of baseboards on a circuit will draw the sum of these amps. Keep the load under 80% of the amperage rating of the breaker.
At 120 volts it will pull 4.166 amps. At 240 volts it will pull 2.08 amps.
Yes, a 30 amp double pole breaker would be suitable for a 4800 watt wall heater. Since watts equals volts multiplied by amps, this wall heater on a 240-volt circuit would draw 20 amps (4800 watts/240 volts), which is less than the 30 amp capacity of the breaker.
Current in amps = watts/ voltage in volts. If you have a 240 volt supply, it will draw 4800/240 = 20 amps, so no. This is a very powerful water heater, and would normally be wired into a dedicated circuit, presumably with a 30 amp breaker.
To determine the hydro usage of a 4800-watt heater, you would need to know the length of time the heater is running. For example, if the heater runs for 1 hour, it would use 4.8 kWh (4800 watts x 1 hour = 4800 watt-hours = 4.8 kWh) of electricity. You can calculate the usage by multiplying the wattage of the heater by the number of hours it is in operation.
To calculate the amperage, you can use the formula: Amps = Watts / Volts. In this case, a 400-watt heater cartridge at 240 volts would draw 1.67 amps.
Yes, a 1500 watt heater operating on 120 volts has an amperage of A = W/V. Amps = Watts/Volts = 1500/120 = 12.5 amps. It is not a recommended practice to do so.
To calculate the breaker size for a 1500-watt 120-volt heater, use the formula: Breaker size = Power (Watts) / Volts. In this case, 1500 watts / 120 volts = 12.5 amps. Therefore, you would need a 15-amp breaker for a 1500-watt 120-volt heater to allow for a safety margin.
Yes but you will not get the full watt rating out of the tank. Watts = amps x volts. Say the tank draws 20 amps. 20A x 240V = 4800 watts. 20A x 208V = 4160 watts. It will take longer to heat your water with less wattage.
Watt volts is not an electrical term. Watts are the product of amps times volts.
No, a 1000-watt electric heater operating at 110V will produce the same amount of heat as a 1000-watt heater operating at 220V. The power output (in watts) determines the amount of heat produced, not the voltage.
To calculate the amperage, use the formula: Amps = Watts / Volts. In this case, it would be 2400 watts / 240 volts = 10 amps. Therefore, the water heater would draw 10 amps of current.
That depends on circuit voltage. 1 watt is equal to 1 volt times 1 amp.
For a single phase circuit, the equation you are looking for is I = W/E. Amps = Watts/Volts.