This will pull 20 Amps continuous so you will need a 30 A breaker and 10 AWG wire. You would have Black, Red, White and Ground. The 240 V would be on the black and red connected to the output from a two pole 240 A breaker. White would be neutral and green or bare wire would be ground.
Yes but you will not get the full watt rating out of the tank. Watts = amps x volts. Say the tank draws 20 amps. 20A x 240V = 4800 watts. 20A x 208V = 4160 watts. It will take longer to heat your water with less wattage.
Watts = Current x Volts with your resistive heat application. To figure out resistance you need to know voltage and current. Since you are drawing 6 amps then Volts = 325/6. This means that there is about 54 volts supplying the heater which seems like a very strange supply voltage. Since Volts = Current x Resistance the resistance = 325/36.
about 4800 watt but should not use it 100% so to be safe 4000 watt (80%)
Each baseboard heater will draw a little over 4 amps at 120 volts or 2 Amps at 240 volts. The total number of baseboards on a circuit will draw the sum of these amps. Keep the load under 80% of the amperage rating of the breaker.
At 120 volts it will pull 4.166 amps. At 240 volts it will pull 2.08 amps.
Yes, a 30 amp double pole breaker would be suitable for a 4800 watt wall heater. Since watts equals volts multiplied by amps, this wall heater on a 240-volt circuit would draw 20 amps (4800 watts/240 volts), which is less than the 30 amp capacity of the breaker.
Current in amps = watts/ voltage in volts. If you have a 240 volt supply, it will draw 4800/240 = 20 amps, so no. This is a very powerful water heater, and would normally be wired into a dedicated circuit, presumably with a 30 amp breaker.
The recommended voltage for a 4500 watt water heater element is typically 240 volts.
Your term "hydro" is another term for kilowatt hours. So to answer your question a 4800 watt heater on for an hour would consume 4.8 kilowatt/hours. To take it further if you knew what you pay for a kilowatt hour in your area, multiply it by 4.8 and you could see how much it costs you to operate the heater. An example if you pay .11 cents a kilowatt hour, the price would be .528 or 53 cents an hour.
The formula you are looking for is I = W/E.
Yes, a 1500 watt heater operating on 120 volts has an amperage of A = W/V. Amps = Watts/Volts = 1500/120 = 12.5 amps. It is not a recommended practice to do so.
To calculate the breaker size for a 1500-watt 120-volt heater, use the formula: Breaker size = Power (Watts) / Volts. In this case, 1500 watts / 120 volts = 12.5 amps. Therefore, you would need a 15-amp breaker for a 1500-watt 120-volt heater to allow for a safety margin.
Yes but you will not get the full watt rating out of the tank. Watts = amps x volts. Say the tank draws 20 amps. 20A x 240V = 4800 watts. 20A x 208V = 4160 watts. It will take longer to heat your water with less wattage.
Watt volts is not an electrical term. Watts are the product of amps times volts.
No, a 1000-watt electric heater operating at 110V will produce the same amount of heat as a 1000-watt heater operating at 220V. The power output (in watts) determines the amount of heat produced, not the voltage.
Watts = Amps x Volts for a resistive load like a water heater.
That depends on circuit voltage. 1 watt is equal to 1 volt times 1 amp.